    Venting a new shower
    I am installing a shower in a basement bath. The bathroom was roughed in for a tub with a 1 1/2" drain, but when the concrete slab was poured, they filled the tub drain box with concrete so I am left with a solid block of concrete where that drain was to be.

    I am installing a fiberglass shower stall 24" to the left of that unusable tub rough in, using 2" PVC. The toilet is locate 48" from this new shower drain, and the toilet is vented through a 2" dry vent.

    I intend to tie the shower drain into this toilet vent line. I will use a wye fitting and slope the drain at 1" over the 48".

    Is it a problem venting this way?

    Thanks
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #2

    Apr 10, 2009, 02:06 PM
    Hi Rghoch...

    Sounds like you have this one nailed! If you pipe this as you suggest, you will be WET VENTING The shower. Here, the toilet vent will act as a vent for the shower as long as the toilet vent remains 2" until it connects into another 2" vent above... ;)

    The wye fitting is crucial as is the 1/4" pitch per foot.

    Let me know if you have more questions...

    MARK
    RG Hoch's Avatar
    RG Hoch Posts: 6, Reputation: 1
    New Member
     
    #3

    Apr 11, 2009, 10:01 AM
    Thanks,

    The 2" vent line from the toilet is 2" all the way until it tie into another 2" vent line.

    Why do you say the wye fitting is critical? I intended to use a 2" Sanitary tee to tie into the vent line.



    Quote Originally Posted by massplumber2008 View Post
    Hi Rghoch...

    Sounds like you have this one nailed!! If you pipe this as you suggest, you will be WET VENTING The shower. Here, the toilet vent will act as a vent for the shower as long as the toilet vent remains 2" until it connects into another 2" vent above...;)

    The wye fitting is crucial as is the 1/4" pitch per foot.

    Let me know if you have more questions...

    MARK
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #4

    Apr 11, 2009, 10:11 AM
    I intended to use a 2" Sanitary tee to tie into the vent line.
    Will this san tee be located above or below the slab? Cheers, Tom
    RG Hoch's Avatar
    RG Hoch Posts: 6, Reputation: 1
    New Member
     
    #5

    Apr 11, 2009, 11:06 AM
    The tee will be below the slab in an 8" void above a sand base. (The slab was poured over a void box which, over the years has deteriorated and left a void beneath the slab.) I have cut through the slab and have access to the vent line where it rises out of the fitting below and behind the toilet. Is there a difference between using a sanitary tee and a straight tee?

    Thanks

    QUOTE=speedball1;1659108]Will this san tee be located above or below the slab? Cheers, Tom[/QUOTE]
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #6

    Apr 11, 2009, 01:30 PM
    RG Hoch...

    You can't use a sanitary tee fitting to connect a drain line on the horizontal... against all plumbing codes. You must use a wye fitting and 45s to get to the new shower drain if you are connecting on the horizontal.

    You can use a sanitary tee fitting on the vertical, however, but that would require the drain line to be buried pretty deep.

    Let us know more...

    MARK

    P.S.: In waste and vent work there is no straight tee fitting... we call them sanitary tee fittings.
    RG Hoch's Avatar
    RG Hoch Posts: 6, Reputation: 1
    New Member
     
    #7

    Apr 13, 2009, 05:55 PM
    Quote Originally Posted by massplumber2008 View Post
    RG Hoch...

    You can't use a sanitary tee fitting to connect a drain line on the horizontal...against all plumbing codes. You must use a wye fitting and 45s to get to the new shower drain if you are connecting on the horizontal.

    You can use a sanitary tee fitting on the vertical, however, but that would require the drain line to be buried pretty deep.

    Let us know more...

    MARK

    P.S.: In waste and vent work there is no straight tee fitting...we call them sanitary tee fittings.
    Thanks for the guidance. I can use a 45 and a wye, no problem.

    Bob

    Quote Originally Posted by RG Hoch View Post
    Thanks for the guidance. I can use a 45 and a wye, no problem.

    Bob
    Just to close out the entire subject, I dug more of the sand out beneath the slab and, lo and behold, the original 1 1/2' tub drain dropped down into a 2" drain reducer, then the 2" PVC connected into the waste stack.. I cut the old 1 1/2" tub drain out and tied the shower drain into the 2" drain.
    I didn't have to mess with the vent at all, and it works great.

    Thanks for all your help, fellows.

    Bob

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wet venting a shower and toilet [ 7 Answers ]

I'm in the process of remodeling a bathroom and need help with venting all of the fixtures (toilet/shower/lav). I was thinking on wet venting the shower and toilet from the lav's vent see the sketch below. I was told that this is possible (up to "code") if a 4" drain pipe is used for the water...

Separate shower and tub venting [ 4 Answers ]

Background: Remodel work, bathroom. Double vanity relocated, broke up shower/tub to separate units. Sinks share one dedicated 2" vent to roof. All bath fixtures drain into a common 3", 1/4" per ft sloped horizontal (via long turn 3x3x2 wyes) then vertical 4" main. Large crawlspace where all drains...

Venting a shower... [ 2 Answers ]

Hello! Some of you may rememebr me form the moving a toilet thread from 2 weeks ago. I am swapping the locations of the toilet and shower. The old shower drain/vent is now removed/capped where necessary, and the new toilet drain/vent is in place. I now need to add a shower drain/vent where the...

Shower venting [ 3 Answers ]

Need to move my old bathtub drain to previous center area of tub for new shower. The new shower drain is 2". The toilet 3" drain is too close -7 in- to put in fittings unless I attach sort of upstream- flow would be in a U. 2 in drain from sinks is 2ft away. Can I put shower connection on this...

Toilet/Shower - Venting [ 1 Answers ]

I am remodeling 2 bathrooms into one. I am moving a few things around, but my question is. I had a 3" vent that went up a wall in between the 2 bathrooms, well I had to do away with it. It was at the end of the line of the rough in and 2 toilets were connected right near it. My question, there...


View more questions Search