    Wiring a goodman heatpump
    How to connect low voltage wires from condensing unit ,thermostat and air handler with electric heat strip
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #2

    Mar 18, 2009, 01:55 PM
    Don't you have the installation literature for the equipment? That would be the best resource if available.
    jaburke's Avatar
    jaburke Posts: 5, Reputation: 1
    New Member
     
    #3

    Mar 18, 2009, 04:10 PM
    Quote Originally Posted by KC13 View Post
    Don't you have the installation literature for the equipment? That would be the best resource if available.
    I purchased this equipment from a home owner that used it for 6 months. He replaced it with a higher seer unit. He misplaced all the literature on this system.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #4

    Mar 18, 2009, 07:10 PM
    Have you already installed the equipment? This is somewhat tricky territory - do you know how the system was uninstalled? Was the refrigerant pumped down and isolated within the outdoor unit, or recovered? Are the other components (indoor coil) sealed? If the equipment is already installed, was proper evacuation performed? Was a bi-flow filter/drier installed? This may seem like a lot of questions - because it is. As far as the control wiring is concerned, I need a little more info before I can help you. The thermostat - what terminal designations (letters) are present? Is it a electronic/digital type, or mechanical/analog type? How many/what color control wire connections are present at the indoor and outdoor units? P.S. Welcome to HVAC 101... ;)
    jaburke's Avatar
    jaburke Posts: 5, Reputation: 1
    New Member
     
    #5

    Mar 18, 2009, 07:58 PM
    System was pumped down and all refrigerant lines were plugged. I reconnected the copper lines, pulled a vacuum down to 29 inches. Thermostate is a white rogers IF58W-72
    jaburke's Avatar
    jaburke Posts: 5, Reputation: 1
    New Member
     
    #6

    Mar 18, 2009, 08:09 PM
    System was pumped down and all refrigerant lines were plugged. I reconnected the copper lines, pulled a vacuum down to 29 inches. A suction line filter drier and liquid line filter drier were added. Thermostate is a white rogers IF58W-72 terminal are G, R, L, X1 ,E ,B, W2, Y,O . Goodman Heat Pump , 4 Low voltage wires, R, W2, O, BL/common. Goodman air handler model aruf4860 with 10 kw heat kit. 5 low voltage wires, Red,Blue ,Green ,White, Brown.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #7

    Mar 19, 2009, 03:51 AM
    A suction filter can only be used with a heat pump system in the cooling mode to clean up a burnout, then must be removed. Operating the system in heating reverses vapor flow, which will be hot, and risks displacement of dessicant. Suction filters are not designed for this. There should be at least 5 wire connections at the outdoor unit - where is the "Y" circuit?
    jaburke's Avatar
    jaburke Posts: 5, Reputation: 1
    New Member
     
    #8

    Mar 19, 2009, 08:12 AM
    There are 5 low voltage wires r,y,w2,o ,bl/com. The reason for the suction line filter drier is that I live in an under ground house and I will never need to run the system in heat mode. The temperature in my house never drops belew 65 degrees, even when outside temperature drops below 20 degrees. I just wanted to know for my benefit if when a house is in need of heat that it was wired correcty. This is the way it think it should be wired. R-from Stat, air handler and heat pump are all wired together. O- from Stat is wired to O- on heat pump. Y- on Stat is wired to Y- on heat pump. C/com from Stat, air handler and heat pump are wired together. W2 on stat and W2 heat pump are wired together with W on air handler an also a wire from W is wired to emerg heat on Stat. I do not think this heat pump has an out door stat,but if it does should be wired in series with the W -wires. If I ever decide that my old bones need some heat ,I will remove the suction line filter/drier. Thanks for your help. jaburke
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #9

    Mar 19, 2009, 11:21 AM
    ((quote))If I ever decide that my old bones need some heat ,I will remove the suction line filter/drier. Thanks for your help. jaburke

    And at that time you will have to go through the whole deal of recovering the refrigerant,removal of filter/drier,pumping down the system all over again.
    Sounds like a lot of trouble and expense,, GOODLUCK
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #10

    Mar 20, 2009, 03:30 AM
    Sounds reasonable, but I would throw in these 2 wrinkles: 1) Use a non-heat pump thermostat and wire only the "R", "W", "Y", "G", and if necessary, "C" circuits to it. 2) Ditch the "O" circuit from the thermostat, and wire "O" to "R" at the outdoor unit, to assure the reversing valve is always in the cooling mode/position.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Trane Heatpump AC Thermostat Wiring [ 3 Answers ]

Hello I'm trying to connect a Trane Weathetron Heat Pump (Model TWX724A100A1) To a Honeywell RTH 7400D Programmable Thermostat. This is a new installation, so there is no previous installation to observe the wiring from. Currently, the wires that we have from the outside unit are as...

Goodman heatpump [ 3 Answers ]

May be a dumb ? But new to me. Does a heat pump run in the same pressures even if its in heat mode? I have a unit low on freon charged it as much as possible.. outside temp is 50 degrees. The highest the low side would go would be about 28 degrees on the r-22 gauge. Is that normal or should it get...

Goodman Heatpump Blower Intermittent ON [ 1 Answers ]

I have a Goodman (Janitrol) Model # CPE36-1AB heatpump cooling AC system about 14 years old (new in 1992). The outside unit comes on in heat mode but the blower sometimes doesn't come on in the air handler . I can feel the insulated pipes leading into the evaporator are hot in the air handler and...

New wiring of heatpump split system [ 2 Answers ]

My house trailer has only electric heat. I have added the "A" coil and heatpump. I have replacaed the two wire thermostate cable with a five wire cable. One goes from the thermostate to the furnace the other goes from furnace to the outside unit. I'm using the two heaters as the aux heat. I have...