I have a Carrier 58GS furnace. It appears to be operating fine until I stood next to it.
The gas flame comes on and off about every 5 seconds. This is not to be confused with short cycling. The blower is running as it should be and at the appropriate times. Thought before I dug into it, the forum may already have the answer.
Thanks for any help,
Bob
|
|
 |
Ultra Member
|
|
Mar 16, 2009, 09:10 PM
|
|
Try cleaning the flame senser,, is located near the burners,don`t confuse it with the igniter
|
|
 |
New Member
|
|
Mar 16, 2009, 09:28 PM
|
|
 Originally Posted by wmproop
try cleaning the flame senser,,,,,is located near the burners,don`t confuse it with the igniter
Thanks wmproop, I'll give it a shot.
|
|
 |
New Member
|
|
Mar 16, 2009, 10:17 PM
|
|
Is your Carrier 58GS equipped with a "standing pilot" ignition system, or does your furnace have a "electronic spark ignition"system?
|
|
 |
New Member
|
|
Mar 17, 2009, 04:19 AM
|
|
 Originally Posted by white732
Is your Carrier 58GS equipped with a "standing pilot" ignition system, or does your furnace have a "electronic spark ignition"system?
Electronic Spark, I miswrote earlier, it is a 58DR
|
|
 |
Heating & Air Conditioning Expert
|
|
Mar 17, 2009, 05:45 AM
|
|
If you have a 3 wire pilot that can be the cause.
|
|
 |
New Member
|
|
Mar 17, 2009, 05:52 AM
|
|
Bob, your pilot assembly would be the first starting point, it's the cheapest and first place to start. After 20 years it's the primary cause for your problem.
|
|
 |
New Member
|
|
Mar 17, 2009, 05:55 AM
|
|
Bob, I miss wrote. I have retired with 20 years in the field and found your type of pilot will cause your problem.
|
|
 |
Ultra Member
|
|
Mar 17, 2009, 10:21 AM
|
|
Quote;;The gas flame comes on and off about every 5 seconds.
I understood this to mean the pilot was working,, but the flame not staying on in the burners
|
|
 |
Ultra Member
|
|
Mar 17, 2009, 10:23 AM
|
|
Guess I understood the pilot was working but the flame in the burners was going out every 5 seconds
|
|
 |
New Member
|
|
Mar 17, 2009, 11:09 AM
|
|
 Originally Posted by wmproop
guess I understood the pilot was working but the flame in the burners was going out every 5 seconds
The above quote is correct. I cleaned all connections along with the flame sensor. It is working for now. Looks like it is the pilot assembly causing the problem. Won't hurt for me to get a new one regardless. Thanks for all the help and rapid responses. First time on this forum and it was a great experience.
Bob
|
|
 |
Heating & Air Conditioning Expert
|
|
Mar 17, 2009, 12:01 PM
|
|
The old 3 wire pilot will allow contact for a few seconds then drop out the gas valve then make connection again. This has been a longstanding problem with the 3 wire pilots. Years ago we used to adjust them in the field but no more just replace. All during this time the pilot will be on.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Carrier 58DHC075 furnace ignites but flame goes out
[ 2 Answers ]
I have a Carrier natural gas furnace. Model 58DHC075-HC
I think it is 92000 BTU. It was made aroung 1990
The furnace ignites OK, but then after a few seconds the flame foes out.
I guess this might be due to a faulty flame detector. Is there any way I can be sure of thuis befoire I order a...
Carrier 58ss cycling
[ 83 Answers ]
I had about the same problem last heating season. One repairman said it needed a new control board and then online I read about the pilot ignitor. I replaced stark electrode and pilot burner and it seemed to fix it. The it started again so since I bought the control board online previous, I put...
Flame cycling!