    Basement bathroom wiring
    Finally putting a bathroom in the basement and here is what I'll be submitting to the builing inspector.

    I've got one open space in my panel and plan on putting a 20/20 tandem breaker in with 12/3. One of the circuits will go to a GFCI on the wall behind the toilet to run the pump (9amps) and then to an outlet by sink. The other circuit will run a floor warming system (5 amps) and the jacuzzi tub (10amps). I will be grabbing power from an adjacent room for the 3 wall sconces and sink light and from another adjacent room for the ceiling fan. It might be hard to visualize but do you guys see any problem with this?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Mar 15, 2009, 10:42 AM
    Since you only have one full size slot in the breaker, using a tandem breaker for the additional circuits using #12-3 will only work by converting at least two other full size breakers to tandem.

    The one slot you have only will allow connection to one leg of the panel, and the new tandem must connect to both legs, when using two circuits and a shared neutral in a #12-3 cable.

    Re-arranging the breakers to get one tandem onto both legs may be a challenge. You can use the new tandem in the one available slot ONLY if you use #12-2 cable for each new circuit feeder.
    coach78's Avatar
    coach78 Posts: 45, Reputation: 1
    Junior Member
     
    #3

    Mar 15, 2009, 07:37 PM
    OK, found out I may have jumped the gun a bit as the whirlpool tub needs a dedicated circuit with a gfci breaker so does the floor warmer so I'm going to have to do some juggling. Maybe put a couple tandems in (I can put up to three in my box). Thanks for the advice.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

New basement bathroom [ 5 Answers ]

I am starting to finish my basement bathroom. When the house was built the basement was plummed for a bathroom. If you are facing the East wall right - left, I have a 2" PVC running vertical(apparently for vanity), toilet drain, 1.5" PVC (unsure, possible toilet or shower vent), cut out and 2"...

Bathroom in Basement [ 3 Answers ]

I just bought a new home and the Basement has a place for the toilet and one drain pipe coming out of the concrete. There is also a vent pipe in the wall. My question is- How can I use the existing drain pipe to add both a shower and a sink? Do I need to bust the concrete and add another drain? ...

Bathroom plumbing with basement bathroom [ 1 Answers ]

Could you please tell me what cause my upstairs bathroom to back up into my basement bathroom?

Bathroom in basement [ 2 Answers ]

Hello, My question is about a bathroom I am building in my basement. It is a new house and came with a stub for the bathtub and next to it is one for the toilet, in between both of them is a PVC pipe that comes from the ground up through the wall and on up stairs. I think this is a vent. My...

Basement Bathroom [ 6 Answers ]

I had my contractors plumber rough in a shower/toilet/vanity in my basement before the floor was poured and Im looking at finishing it off. I have done some plumbing projects before but have never seen or dealt with a basement project. I have 3 pvc pipes, 1 for the toilet, 1 for the sink and 1...


View more questions Search