Finally putting a bathroom in the basement and here is what I'll be submitting to the builing inspector.
I've got one open space in my panel and plan on putting a 20/20 tandem breaker in with 12/3. One of the circuits will go to a GFCI on the wall behind the toilet to run the pump (9amps) and then to an outlet by sink. The other circuit will run a floor warming system (5 amps) and the jacuzzi tub (10amps). I will be grabbing power from an adjacent room for the 3 wall sconces and sink light and from another adjacent room for the ceiling fan. It might be hard to visualize but do you guys see any problem with this?