    Roughing on for bar sink drain
    I am trying to find code for roughing in the bar sink drain. I know I can run the pipe from the bathroom vent (vanity) and have determined the height I would need is 27" sloping downward to 26-1/2". I cannot find any code stating I can or cannot have the drain that high. Does anyone know if there is code for this?

    Thanks
    Milo Dolezal's Avatar
    Milo Dolezal Posts: 7,192, Reputation: 523
    Plumbing Expert
     
    #2

    Mar 7, 2009, 01:55 PM

    Your question is a bit vague and confusing. I don't know whether there is Code for height of the sink drain inlet. That dimension is determined by the height of the sink, not by Code. Drain inlet should be anywhere between 17-21" from the floor. For pedestal sinks, you have to place it according to the leg cut-out.
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #3

    Mar 7, 2009, 02:28 PM
    Quote Originally Posted by CodeChaser View Post
    I am trying to find code for roughing in the bar sink drain. I know I can run the pipe from the bathroom vent (vanity) and have determined the height I would need is 27" sloping downward to 26-1/2". I cannot find any code stating I can or cannot have the drain that high. Does anyone know if there is code for this?

    Thanks
    Milo, He's asking about va bar sink not a lavatory but the rough's about the same. Tom
    CodeChaser
    I really don't understand your question. Are you saying that the elevation of the stubout will be 27 inches off the floor with a 2 foot run down to a sanitary tee in the vent? Here's where I run into a problem with your figures.
    The average bar sink will set 32 inches from floor to rim. Since the average depth of a bar sink's about 8 inches. That puts your stubout about 3 inches into the bow itself.
    As a rule we rough our bar sink at 18" off the floor to the center of the stubout.
    Where did you ever come up with 27" off the floor and why does code concern you? Will a permit be pulled and will the job be inspected?
    More questions? I'm as close as a click. Regards, Tom
    CodeChaser's Avatar
    CodeChaser Posts: 3, Reputation: 1
    New Member
     
    #4

    Mar 8, 2009, 05:18 PM
    Thanks for the answers and sorry for the confusion. What I am trying to do is finish my basement. On one wall I would like to place a small L-shape bar, with a samll sink, herein lies the problem. The closest drain is the one for the full bath down staris and the only way I can tap into it is to go up 26-1/2" because of the way the drain for the bathroom vanity is set and the pipes coming off for the P-trap. I have a run of about 5' and then a 60 degree elbow followed by a 2' run. to be safe I would raise the P-trap for the new bar sink to 27" (1/2" for drain slope) but am not sure if this will work. I have a small 6 inch bar sink purchased from Lowe's and I did the calculations for the P-trap and believe it will work by the skin of my teeth, but am not sure whether I need to worry about code when I have the final inspection for the basement or not. I know this is a lot of information (none sense), but hope it helps
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #5

    Mar 9, 2009, 05:45 AM
    One more time,
    The average bar sink will set 32 inches from floor to rim. Since the average depth of a bar sink's about 8 inches. That puts the bottom of the bowl at 24" and your stubout of 27" about 3 inches into the bow itself
    The only way 27" would work is if you raised the coumter top.
    There's another problem,
    I have a run of about 5' and then a 60 degree elbow followed by a 2' run.
    No mention bof a vent. If the drain pipe's 1 1/2" you wi;ll have to run a vent off the drain line within 3 1/2' from the trap. If the drain line's 2" then you have 5' before you must vent the line. This is code in most areas.
    Unless I've misunderstood the entire thing you either lower the stubout or raise the countertop. Did I miss anyrhing? Tom

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Relocating Sink Drain/Vent to Dedicated Stack Serving Kitchen Sink & Dishwasher [ 3 Answers ]

I am relocating an upstairs vanity sink from one wall to another (also going from single to double bowl). Rather than relocate the drain and vent pipe, I am hoping that I can tie into a 1-1/2" copper vent pipe that is located right behind the vanities intended location. The copper vent pipe is from...

Hooking a Utility Sink in basement to Kithcen sink drain [ 2 Answers ]

I'd like to install a utility sink in the basement and have attached a drawing illustrating the current piping and proposed attachment. Basically, the kitchen sink drain goes directly into a drain in the basement floor via a 1-1/2" steel pipe, which is tied to the sewer system. I'd like to put a...

Roughing in drain lines in basement floor [ 1 Answers ]

Please help on roughing in drain lines in basement

Roughing In a Drain for a Shower [ 4 Answers ]

I'm currently working on remodeling a bathroom on my first floor which sits directly on the concrete slab. Part of the remodeling included making a 32"x32" shower into a 32"x48" shower. I've removed the old fiberglass shower pan and currently have the old drain sticking up from the slab. I...

Kitchen Sink/Laundry Sink Drain Vent Non-exist [ 3 Answers ]

The set-up from kitchen sink leading down to drain to basement: 1. Kitchen sink - (R side) - connected to a P drain I think you call it -PVC-, connected to a "metal" T, which has a Studer vent gizmo attached to the top of it, then draining into a metal pipe straight down to the drain in the...


View more questions Search