    Goodman GMP100-3
    Hi,

    Have a Goodman GMP100-3 that's acting strangely. Here's the scenario:

    - Thermostat calls for heat
    - Inducer starts
    - Vacuum switch pulls in
    - Furnace fires
    - Furnace comes up to heat and blower starts
    - Ignition cuts out as blower starts
    - Ignition sequence restarts and building is heated.

    Seems strange to me that the flame trips out as the blower starts and then re-ignites and continues normally.

    Any thoughts?

    Thanks
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #2

    Mar 7, 2009, 06:20 AM
    Connect a voltmeter to the unit incoming power supply (use analog if available) and observe it during start-up. If the voltage spikes dramatically when the blower is powered, turn power off and check all electrical connections through power supply circuit. Pay particular attention if the supply circuit is aluminum. Also, inspect circuit board for any evidence of overheating/burning or moisture exposure.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Goodman GMP100-3 Furnace won't Stay On. [ 14 Answers ]

Hello, I have a Goodman Furnace (model # GMP100-3). The furnace will not stay running. Here is the sequence of events for two different scenarios that are occurring. Scenario 1 1. Thermostat Calls for Heat 2. Inducer starts 3. Pressure switch closes 4. Heating element glows 5. Burners...

Goodman GMP100-4 blows hot air [ 3 Answers ]

The indicator light on the control panel blinks four times. The cover panel says that 4 blinks is either limit switch open or auxiliary switch open. We replaced this control board in October 07. Do we need to replace the board again? Is it possible that the board is wired incorrectly? Does...

Goodman GMP100-4 blows cold air [ 4 Answers ]

Hi, I have a GMP100-4 that blows cold. The pilot light is on and the burners burn but only for a few seconds before turning off again. The blower is on all the time so I'm getting little to no heat around the house. I've replaced the filter, I assume there is only one and it is situated...

Wiring inline duct fan to furnace fan goodman gmp100-4 [ 2 Answers ]

How do I wire my inline duct fan to my Goodman model gmp100-4 gas furnace fan so that the inline duct fan comes on and off when the furnace fan does? I understand that I need a relay from the inline duct fan but don't know where to connect the relay to the furnace.

Kenmore GMP100-4 [ 1 Answers ]

I have a Kenmore furnace (I assume it's made by Goodman), model GMP100-4, 1993. The initial problem was that the furnace only operated intermittently, it would run most of the day and then stop. I had to turn the furnace off to get it to operate again. After a few days of this this the furnace only...


View more questions Search