What size manifold do I need?
What size manifold do I need to supply water to five 1.6(gpm) Water closet, Tank, One Piece; one Urinal, Valve 15(gpm), one Lavatory 4(gpm) and one Drinking Fountain Flow Rate 0.75(gpm)?
|
|
 |
Home Repair & Remodeling Expert
|
|
Mar 2, 2009, 05:33 PM
|
|
3/4" pipe should be all that's needed, then use 1/2" to each fixture. Keep in mind that all fixtures will not likely be in use at the same time. I think you are missing a decimal point on that urinal flush rate.
|
|
 |
Eternal Plumber
|
|
Mar 2, 2009, 05:48 PM
|
|
I would come off a 1" main with 3/4" manifolds feeding not over 3 fixtures off a 1/2" branch. Good luck, Tom
|
|
 |
Senior Plumbing Expert
|
|
Mar 2, 2009, 06:23 PM
|
|
Hi all:
Just to make this clear: A urinal in itself requires a 3/4" feed. I am sure that Bob simply forgot this... ;)
As Tom stated, a 1" pipe manifold should do the job here... :) (3/4" to the urinal, 1/2" to each toilet, 1/2" cold (and 1/2" hot) to the lavatory and 1/2" to the drinking fountain).
MARK
|
|
 |
Plumbing Expert
|
|
Mar 2, 2009, 06:27 PM
|
|
Is this commercial job ?
|
|
 |
Senior Plumbing Expert
|
|
Mar 2, 2009, 06:31 PM
|
|
Commercial or not Milo... still requires 1" minimum cold water pipe.. ;)
Let me know what you are thinking here...
MARK
|
|
 |
Plumbing Expert
|
|
Mar 2, 2009, 06:34 PM
|
|
I disagree with you Mark, If this is a commercial project than each plumbing fixture requires 3/4" , type L, supply. Urinals / flush valves may be 1", therefore they would require 1" supplies. Therefore, depending on developed length of the supply pipe for the fixtures given - the supply should be more like 1 1/2".
|
|
 |
Senior Plumbing Expert
|
|
Mar 2, 2009, 06:36 PM
|
|
If the toilets are flushometer type toilets then I absolutely agree with you Milo... but most commercial applications in my area are now using typical floor-mount toilets so only need a 1/2" line to each... ;)
I see where you were going...for sure!
Mardin... we need more info. Here... commercial or residential? Let us know?
Milo, do they allow floor-mounted toilets for commercial application in your area..? And I have never seen a 1" urinal flushometer..???
Milo...
Mardin did say "five 1.6(gpm) Water closet, Tank, One Piece"... why I stated the size as confidently as I did... ;)
|
|
 |
Plumbing Expert
|
|
Mar 2, 2009, 07:34 PM
|
|
Mark, Yes, they allow floor mounted commercial toilets with tank. However, they are not too popular bcs they are constantly broken (people flush with their foot )
Yes, 1" flush valve is common (Zurn, Sloan) - at least here...
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Pex Manifold hot/cold chambers
[ 5 Answers ]
I searched as many topics as I could to find the answer to my question, but couldn't find anything. I have a vangard manabloc (Pex manifold) I have two chambers, hot/cold, both with 9 hookups, the 7 on the top are for 3/8" and the two on the bottom are for 1/2". The hot side has all red tags,...
Water pressure using PEX manifold
[ 3 Answers ]
I am getting ready to re-plumb my entire house. I plan to switch from Copper to PEX. The reason is that I have a well and the water causes pinhole leaks in the copper. My question is:
The current setup is a standard tee and branch. I have 1/2" pipe coming off of the 3/4" mains in the...
Manifold on peugeot 806
[ 1 Answers ]
I have a peugeot 806 and bought new bolts to join the down pipe to the manifold but have more parts to it than what I have does anyone have an exhaust diagram or picture showing how these are fitted many thanks if you have
Pex manifold
[ 1 Answers ]
I am adding a new bath and using pex to plumb the supply lines. It is only 10 feet from the hot water tank. All the existing supply lines are 1/2 inch copper right from the meter which is 35 feet at the other end of the house. Question is all the manifolds I see have a 3/4 inch inlet. Will I...
CPVC manifold?
[ 3 Answers ]
I've read that PEX manifolds can be used to reduce energy costs by reducing the amount of water that must be flushed from the lines each time hot water is requested. I prefer working with cpvc rather then PEX and I'm wondering if the same efficiency could be achieved by creating a cpvc manifold...
View more questions
Search
|