    Sub-panel sizing of wire
    Have an existing 100 amp service. Wish to install a 70 amp sub-panel. What size wire should be used? Distance to sub-panel is 45 feet.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Feb 23, 2009, 12:50 PM

    #4 will work, #2 will reduce voltage drop.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Feb 23, 2009, 02:16 PM
    #2 is extreme overkill at only 45'.
    Voltage drop is not even close to an issue at 45', even at full load amperage.

    Why do you need 70A? Using #6cu you can go with 60A and the wire will be much cheaper. If you do go with #4 you can use a 90A feeder breaker, or even 100A in some cases.

    If you must have a 70A breaker then you must use #4cu.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #4

    Feb 23, 2009, 02:21 PM

    If this was my Shop, I like a little overkill. Plus, I could easily upgrade to a 100 Amp Panel. I have no idea of other losses/lengths involved.
    #4 will work.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire sizing and conduit sizing [ 8 Answers ]

I am looking for confirmation on some of the info I have found and answers to a few missing pieces. This is regarding wire size and conduit size for service conductors from the meter to the breaker panel (about 30 ft away). Wire Size: 125A service needs #2 copper or 1/0 aluminum -- #6 copper...

Wire Sizing [ 2 Answers ]

I am rewiring a house in Mexico and following the 2002 NEC for wire sizing, grounding, circuits, etc for all work from the meter on. Service panel is 125A and will support air condition along with all other lighting and appliances. The utility company will only supply a 6 AWG overhead triplex...

Sizing Wire [ 3 Answers ]

Im running a new 100amp sub about 40 ft from house. Ive been reading but wanted to know you guys' opinion. Should I go with THWN #3 for my Hots/Neutrals. And #8 for EQ Gnd.? I'm kind of confused about the 90/75 degrees that rate this type wire. Also I understand about having to conduit...

Sizing Main Panel(s) For Home [ 1 Answers ]

I am building a home (could eventually be 8000 sf+) and doing most of the Electrical work myself, but I am working with a electrician not Familiar with my issue. I have around 200 circuits so far, which I Know is much more than usual. I have limited the # of receptacles per Circuit to 6, and...

Wire sizing for sub panel. [ 1 Answers ]

Thank you for the response on my sub panel questions. I finally found a slim line breaker which will work in my main panel. I can now consolidate two breakers to give me room for a 100 ap breaker. This breaker will feed the sub panel in my workshop. I plan on placing a 100 amp sub panel in the...


View more questions Search