-   -   Sub-panel sizing of wire (https://www.askmehelpdesk.com/showthread.php?t=321067)

  • Feb 23, 2009, 12:30 PM
    Jack2
    Sub-panel sizing of wire
    Have an existing 100 amp service. Wish to install a 70 amp sub-panel. What size wire should be used? Distance to sub-panel is 45 feet.
  • Feb 23, 2009, 12:50 PM
    Stratmando

    #4 will work, #2 will reduce voltage drop.
  • Feb 23, 2009, 02:16 PM
    stanfortyman
    #2 is extreme overkill at only 45'.
    Voltage drop is not even close to an issue at 45', even at full load amperage.

    Why do you need 70A? Using #6cu you can go with 60A and the wire will be much cheaper. If you do go with #4 you can use a 90A feeder breaker, or even 100A in some cases.

    If you must have a 70A breaker then you must use #4cu.
  • Feb 23, 2009, 02:21 PM
    Stratmando

    If this was my Shop, I like a little overkill. Plus, I could easily upgrade to a 100 Amp Panel. I have no idea of other losses/lengths involved.
    #4 will work.