    Installing central A/c and heat
    I plan on installing central heat and a/c to an old Jim walters home which is 2 story. I feel that I should have separate units for each floor, but an wobdering if this is cost effective. I am guessing that each level is about 1000 sq ft. The lower is well insulated , but the upper, we feel has very little. I hope to correct this but later this year. I have done no research on this yet, but I am wondering what size unit for each floor? I am in central Texas and I like my house cool. Also if anyone has recommendations as to a brand. I think that the ducts will have to be put in some kind of drop down area for downstairs and possibly the floor for upstairs as there is no attic. There is only about 1 inch between the roof and the ceiling at this time.( when I had the roof installed the roofing nails came through the ceiling.)
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Feb 6, 2009, 08:39 AM
    You need to have a manual J and a Manual D performed to determine exactly what size of equipment will be needed and what size any additional duct work will have to be. Get your insulation work done before the calculations are made.

    Once these facts are known you can get accurate estimates done to reflect the true costs of heating and cooling your home. The estimates can be done so you can see the cost difference between one unit,one unit with two thermostats and a zone damper to allow separate control on both floors of the home OR my preferred solution which is two complete separate systems.

    Brands are all about the same. They all heat and cool it depends upon how fancy you want the equipment to be and how long the warranty lasts.

    The most important thing is the install. A poor instillation can take the most expensive equipment and turn it to junk in short order. The cheapest equipment installed properly will last for many years. Check with the BBB and your neighbors and friends to see who has made them happy with there furnace and A/C work. Stay far away from any company that will not do a Manual J and D for your job. There might be a extra charge for the Jand D work but it will be worth every dollar and more. Your comfort and energy usage is of prime importance especially since the utilitys are so expensive.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Electri Central heat noy putting out any real heat [ 1 Answers ]

My son's condo has central heat and air, but when the heat setting is put on, there is very little heat being produced. The air coming from the registers is barely warm. Trying to get an idea of what the problem might be. He has installed a new thermostat, but that didn't help at all. Thanks

Should I choose central air/heat or ductless air/heat systems [ 7 Answers ]

Hello. I am rehabbing a house which is approx 3100 sq ft including basement. It currently has radiators and no central air. I've been reading about the ductless heating and air systems and the idea of them seem great but are they really better than the forced heat and central air systems? Is the...

My central heat and air won't blow out heat [ 1 Answers ]

Recently, my central air ran out of freon so this summer I couldn't cool my house.Now my Unit will not blow out any heat. I tried to turn the heater on but it smelled like it was trying To catch on fire. All I want to know is do I need to apply freon to get my unit to produce Heat?

Installing Central Heat & Air [ 2 Answers ]

I have a 100 year old, two story ranch house, with NO insulation. Currently all that warms the house is one wall heater and one (seperate) A/C. I want to install a central heat and air unit. My question is: Do I need to install the central Heat and Air PRIOR to putting in insulation? Or can...


View more questions Search