    Premature burner shutoff old furnace with no electronics
    Have an 'old' friedrich furnace (model GU4050NBB) with no electronic controls (which I would be more familiar with). Unit has no inducer, no CO sensors and no flame sensor. Just your basic standing pilot with the electrically controlled gas valve. When the heat call comes, the main burner lights. I can see the fan limit moving as the plenum comes up to temp, but the main burner shuts off before the 'on' limit for the blower. Is this a bad gas valve, poor electrical connections, or something else I'm not familiar with on this old beast?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Feb 3, 2009, 11:09 AM
    Usually the fan control also has a limit device built into it. It is possible that the blower motor itself is not working or the fan and limit control is defective. Jump the fan control to see if the blower motor will run or if the thermostat has a fan on-auto setting turn it to on. This way your will know if the blower motor works.

    If the blower motor works then you know it is good. Now you will have to test the fan and limit control or replace it since it controls the blower motor. I would also check around the furnace to make sure no other control or thermal disc is causing the problem.

    One last item you might try. Many times as controls get old they will loose there setting. Hold the dial and move the fan lever to a cooler temperature. That will cause the blower motor to come on sooner and that might help the situation.
    Attached Images
      
    tmandato's Avatar
    tmandato Posts: 5, Reputation: 1
    New Member
     
    #3

    Feb 3, 2009, 11:22 AM
    Quote Originally Posted by hvac1000 View Post
    Usually the fan control also has a limit device built into it. It is possible that the blower motor itself is not working or the fan and limit control is defective. Jump the fan control to see if the blower motor will run or if the thermostat has a fan on-auto setting turn it to on. This way your will know if the blower motor works.

    If the blower motor works then you know it is good. Now you will have to test the fan and limit control or replace it since it controls the blower motor. I would also check around the furnace to make sure no other control or thermal disc is causing the problem.

    One last item you might try. Many times as controls get old they will loose there setting. Hold the dial and move the fan lever to a cooler temperature. That will cause the blower motor to come on sooner and that might help the situation.
    Wow thanks for the quick response. I failed to include that the blower does come on, but only after the burner shuts down (the dial on the fan limit continues to climb after the burner shuts down). The fan limit never reaches the high safety limit, because once the blower comes on, I can see it 'dialing' back down until it hits the low setting 'off'. I will try lowering the 'on' setting as you suggested and look closer for another hidden limit. If I find one I'll assume that I have a problem with the heat exchanger that is letting hot air blow on the limit and shutting down the burner, but I don't expect to since the wiring is simple and I didn't see any wires straying off to a hidden disc... :) will get back to you with what I find.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Feb 3, 2009, 11:25 AM
    If anyone has played with the wiring of that switch that could also be a problem.
    tmandato's Avatar
    tmandato Posts: 5, Reputation: 1
    New Member
     
    #5

    Feb 3, 2009, 12:19 PM
    OK - here's where I'm at. The fan limit switch seems to operate, though it was a little 'sticky', it operate smoother now just from holding it and adjusting the settings. Following your advice I lowered the 'on' setting to about 115, it had been at 150. This allows me to get a little more heat out of the furnace, but the burner still only burns for about 45seconds, then shuts down, regardless of whether the blower is in an 'on' cycle or not. There are definitely no other limit devices involved. Any more thoughts?

    BTW - the limit switch in question is a honeywell, like the B/W photo you attached...
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Feb 3, 2009, 12:25 PM
    Eliminate the thermostat control to see if that is causing the problem. R and W are the terminals in the furnace. Disconnect one or the other and then Jump R and W together. This will mean that the burner will be on all the time. If the burner runs all the time while jumped then the thermostat is the problem. Post back with results.
    tmandato's Avatar
    tmandato Posts: 5, Reputation: 1
    New Member
     
    #7

    Feb 7, 2009, 10:02 AM
    Sorry for the delay. As soon as I read your post I knew you were right. How did I overlook the simplest solution? I guess because I rarely get an easy fix. Anyway a new thermostat solved the problem. I replaced the fan limit too, since I didn't like it's herky-jerky operation. Thank you so much for your advice.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #8

    Feb 7, 2009, 07:03 PM
    Glad you got it working again.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Oil Furnace.Burner goes out before fan comes on [ 3 Answers ]

Hello, I have a Miller oil furnace Model MSBA-066ABFO-05 that fires up and then shuts down because the fan takes to long to turn on. When this happens the reset trips on the controlor. The fan comes on shortly after the limit trips. When the fan is running if I push the reset the burner fires...

Furnace blower won't shutoff [ 2 Answers ]

My furnace recently started working again, but now the blower won't shutoff after the heating cycle is done. It keeps on going and you can still feel a little bit of heat coming from the vent or w/e (sorry for not knowing the right name for it.)Also it starts to smell like something is burning.

Furnace burner doesn't always come on [ 2 Answers ]

Furnace burner doesn't always come on, so I manually turn the thermostat off/ also turn the temperature setting down, when the furnace shuts off I turn the turn the thermostat back to on/ also turn the temperature setting to the desired room temperature, and then the furnace will usually work...

Furnace burner [ 2 Answers ]

Greetings,I have a tempstar furnace model ntc6075fba1,s/n l984128725, the pilot lights, then the blower comes on but the burner does not come on, then when the thermostat is turned down the blower continues to run.please inform me of the problem.Thank you, Albert.

Oil Burner Furnace [ 1 Answers ]

The problem goes like this. Thermostat calls for heat, burner starts and runs for a minute or so and shuts off. After burner shuts off, the blower starts and the burner starts again until the thermostat reaches temp and the burner shuts off blower contiues to run until the low temp limit is...


View more questions Search