    outer pair of quad breaker: how do both trip together
    I got a new quad breaker (Murray) for two 240V circuits. I noticed that the metal bar that connects the two on the outside ( that is, out of X X X X, I mean the X - - X circuit) works great for turning both on at the same time, but I can flip one of them off and the bar doesn't pull the other one down. Is something horribly wrong, or are these breakers designed with some kind of internal linkage that doesn't depend on the physical switch part to trip open the second one if the first one trips?
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Jan 14, 2009, 03:39 PM

    Weaker half of breaker will trip when a leg hits ground/overloads. Even with an equal load, 1/2 of breaker may not trip at same, due to half being weaker, not exact, The half that trips handles the fault.
    But to work on it safe, you would verify both halfs are switched off.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Troubleshoot: Bathroom Fan causing breaker to trip [ 5 Answers ]

I have just installed a new Panasonic ventilating fan in our bathroom. Model #: FV-08VS1 When I turn on the fan, the breaker trips. Have checked the electrical connections and everything appears to be connected properly. There is no other load on this ciruit.

How Double Pole Circuit Breaker Trip? [ 9 Answers ]

On my electrical service panel, the "MAIN" breaker is a double pole breaker and each side is marked "100 Amps." Does that mean that when the total amperage exceed 100 one side it will trip, or if the total of both sides exceed 100 amps it will trip? Also, I recently bought a new electric range. I...

Circuit Breaker didn't Trip [ 7 Answers ]

I have a 1 year old home. The bathroom outlet is a GFCI outlet on a circuit protected by a 15 amp ARC FAULT BREAKER. Today my wife plugged her hair blowdryer and the base of the cord lit up like an arc welder. This lasted for 5-8 seconds before the cord completely melted and the fireworks...

Circuit breaker failed to trip [ 2 Answers ]

I made a big error today on wiring a new circuit. I pulled 2 cables (for 2 circuits) back to the consumer panel and then connected the wrong cable. The cable that I connected was stripped at the other end but not yet connected to anything. When I went to inspect it, I tugged on it and there was one...

Breaker doesn't trip [ 3 Answers ]

There is a property that has a 30-amp breaker in the electrical distribution panel labeled for the AC unit. The outside HVAC unit had a maximum over-current protection rating of 25-amps. I'm looking to see how serious this is and also to understand why the breaker doesn't trip with that amp...