    Last place to check/is this junction box wired correctly
    To my knowledge this light has never worked. I figure its already mounted why not try to make it work.All tests are good ,bulbs are good,etc.

    Two 14-2 romex cables each coming from two nearby breaker panels that converge at a junction box and are wired into 1 length of 14-2 romex that runs into a box for a motion light. It is wired the following way at the junction box: 3 ground wires wire nutted together,3 neutral wires wire nutted together and the hot wire is pigtailed to each of the hot wires coming from the breaker panels and wire nutted to the hot wire going to the motion light box. All connections test out good and do not have signs of burn marks ,crumbling old wire etc.
    codyman144's Avatar
    codyman144 Posts: 544, Reputation: 31
    Senior Member
     
    #2

    Jan 12, 2009, 10:27 PM
    Quote Originally Posted by lights007 View Post
    Two 14-2 romex cables each coming from two nearby breaker panels that converge at a junction box and are wired into 1 length of 14-2 romex that runs into a box for a motion light.
    That does not make any sense to me. Are you sure it is not one 14/2 wire from the service box and connecting to two wires in the j-box? Why the two breaker panels as you describe? And if they are both connecting to the same wire that feeds the light wouldn't that be a big no no (experts please correct me if I am wrong)?

    Could you please describe a little better or maybe take some pictures?

    Thanks - John
    lights007's Avatar
    lights007 Posts: 2, Reputation: 1
    New Member
     
    #3

    Jan 13, 2009, 07:24 AM
    Quote Originally Posted by codyman144 View Post
    That does not make any sense to me. Are you sure it is not one 14/2 wire from the service box and connecting to two wires in the j-box? Why the two breaker panels as you describe? And if they are both connecting to the same wire that feeds the light wouldn't that be a big no no (experts please correct me if I am wrong)?

    Could you please describe a little better or maybe take some pictures?

    Thanks - John
    Thank you for the reply. The connections made no sense to me either John. One conclusion I did come to is that at one time I was told before I purchased this duplex that the utility bill was shared/split between the two units,and perhaps they were trying to get power from both of the breaker panels to the motion light.Anyway I want to make it right.
    codyman144's Avatar
    codyman144 Posts: 544, Reputation: 31
    Senior Member
     
    #4

    Jan 13, 2009, 10:45 AM

    Than wire it to just one of the incoming 14/2 lines from one of the breaker panels. Than cap the other one off. Do you have a voltage tester or similar device? If so you could use this to verify that you are getting power at the J-Box. If you are and it still doesn't work either the fixture is bad (which could be likely given the improper wiring) or there is a break in the line from the j-box to the light. Need to troubleshoot and narrow down where the problem is.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #5

    Jan 13, 2009, 05:42 PM

    Are you sure that there aren't two motion activated lights?

    First, you would never source the 120 VAC feed from two distinct breakers, period.

    Please obtain a volt/ohm meter and test the one line that feed the pigtails.

    What I am looking for is one and only one constant Hot line.

    Once you find that one line, connect the black from the feed to the black from the fixture. Connect the White from the Feed to the White from the fixture and then connect the Equipment grounding conductors (bare) together.

    Turn the feed breaker back on and test the functionality of the one lamp.

    Next check the same position on the other side of the duplex to see if there is also a motion detector there. If there is verify whether it is working. If it is not, then turn your breaker off and add the second light's line into the pigtails keeping the colors the same.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

2 ceiling fans in one room with 2 light switches not wired correctly [ 4 Answers ]

I have a room with 2 ceiling fans. I have a light switch with 2 switches. Each switch turned on a light on a ceiling fan. The fans worked by using a pull chain on the fan. I decided to install 2 new fans. The new ceiling fans had a white, black, green and blue wire. Ceiling fan fixture one...

220 junction box [ 5 Answers ]

Two years ago, I moved my dryer from one room to another (built a new laundry room). At the time there was a straight run 220 line (it's own double 30-amp circuit). Because of the basement being finished where I could not run an entire new direct line for the dryer I decided to use two-thrids of...

Another Junction Box ? [ 9 Answers ]

Again, thanks to everyone for all their valuable information as I wire up my Recording Studio addition. :) You guys are great! ;) I have another question reference the use of Junction boxes. On a couple of my framed walls, where I wired in outlets, some of the outlets (for like Exit Signs) are...

Ceiling fan not wired correctly [ 4 Answers ]

I and neighbor put in a ceiling fan in the bathroom. It seems that the fan is not blowing the steam out. The fan is designed for a larger bathroom. I'm not a electrician but my thinking is to reverse the wiring to the poles so that the fan will work in the correct direction so that it will blow...

15A off a 20A junction [ 2 Answers ]

Is it OK to take a single 15A line off a 20A branch circuit. Specifically, I have a new 20A kitchen wall circuit which will exist only of two 20A counter GFCI outlets. I have had to rework that wall for the gas stove and want to run a 15A outlet for the gas stove electrics. Can I just take a 15A...


View more questions Search