    20A 12 ga bath circuit to 14 ga for light and fan?
    Hi,
    I have rewired my bath to a dedicated 20A 12ga line. Power goes to a 20A GFCI outlet. Can I run 14 ga from the GFCI to a 20A 3-way light switch and a separate 14 ga to a 20A exhaust fan switch? Both will be pigtailed off the GFCI.
    Thanks a million!
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Jan 6, 2009, 04:51 PM

    Absolutely not! 14 AWG is rated for 15 amp only, not 20 amp.

    If you mix 14 AWG conductors, by NEC code you are limited to 15 amp. You are required to use a 15 Amp breaker.

    You would be much better off using only 12 AWG conductors which are rated at 20 amp.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Jan 6, 2009, 05:36 PM
    And if this is a newly rewired bathroom the receptacle circuit must be on a 20A circuit.

    Just use all #12 and you are fine.
    bolt in blue's Avatar
    bolt in blue Posts: 68, Reputation: 2
    Junior Member
     
    #4

    Jan 6, 2009, 05:49 PM
    Keep in mind that the code today requires bathrooms to be on 20 amp circuits. You're going to want to use all 12 gauge cable and keep the 20 amp breaker.

    Oops! Didn't mean to duplicate the above response! Left this question open a little too long before saving.
    DJRussell's Avatar
    DJRussell Posts: 2, Reputation: 1
    New Member
     
    #5

    Jan 7, 2009, 05:49 PM
    Quote Originally Posted by donf View Post
    Absolutely not! 14 AWG is rated for 15 amp only, not 20 amp.

    If you mix 14 AWG conductors, by NEC code you are limited to 15 amp. You are required to use a 15 Amp breaker.

    You would be much better off using only 12 AWG conductors which are rated at 20 amp.
    Thank you very much for your time and guidance. I knew that ding-dong at work was wrong. Thanks again very much.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bath Light/Fan Wiring [ 2 Answers ]

Hello. I am attempting to switch a double-switch in a single gang box that controls the light and fan in my bathroon to 2 single switches in a double gang box. There are 2 sets of wires coming into the box. One has a black, white and ground. The other has a black, white, ground and red. ...

Replacing Old Bath Light/Fan with New. [ 3 Answers ]

I am replacing an old batroom light fan with new one. Everything seemed fine until I had to do the wiring, I have 2 wall switches on a single plack, One switch is for the light above the lavatory and for the ceiling light, The other switch was only for the fan. The old light/fan wiring had...

Wiring kitchen and bath on same circuit [ 3 Answers ]

1. I am wiring for a future bath and kitchen in my unfinished basement. Can I put the kitchen outlets only and bathroom outlets only on the same GFI protected 20 amp circuit or do I need a separate circuit for each. I am limited on available places to add additional circuits to by main panel. ...

Light and bath fan on one switch [ 4 Answers ]

Hi, I need a little help. I want the bath fan and light to opperate on one switch. I ran the power to the light and have the fan connected at the light. Then I ran the switch to the light.my problem is when I turn the light on, the light is very dim and the fan is at half speed. What am I doing...

Sconce light by bath tub [ 3 Answers ]

I want to install a wall sconce light 5 feet above the bath tub rim. Will this meet code in California? Thanks


View more questions Search