    My Beckett furnace has been running past the thermostat setting. The other night it was 79 degrees, we have it set at 64! Yesterday I went to the store to buy a Primary Control and installed it, and the furnace still keeps running. Ive even checked the thermostat (of course) and we are totally at our wits end... does anyone have any suggestions?

    Dave13
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jan 4, 2009, 07:20 AM
    If you disconnect the thermostat wires from the primary does the burner continue to run? If it does the primary/transformer/burner motor wires are hooked up wrong.
    Dave13's Avatar
    Dave13 Posts: 3, Reputation: 1
    New Member
     
    #3

    Jan 4, 2009, 07:34 AM
    No, I replaced the primary control yesterday and when you remove one of the wires it will shut off. I tried to remove one of the wires from the thermostat and it continues to run.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Jan 4, 2009, 08:22 AM
    Then you have a wiring problem. Get the paperwork for the primary you replaced and wire like it says.
    Dave13's Avatar
    Dave13 Posts: 3, Reputation: 1
    New Member
     
    #5

    Jan 4, 2009, 08:29 AM
    Could it be the limit swtich?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Jan 4, 2009, 08:38 AM
    If you remove the thermostat wires from the primary and the burner does not shut down then the primary is not controlling the burner and associated parts. The prinary relay contacts are burnt together from being hooked up wrong or it is not wired correctly like I said before.

    Disconnect the thermostat wires from the furnace primary control if hooked up there a then see if it shuts off. If not the wiring for the primary is wrong allowing the voltage to pass to the burner with out thermostat control OR the new primary contacts are burnt.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

System does not react to thermostat, thermostat set to off, AC still runs. [ 3 Answers ]

We had a new AC system put in this summer. I turned it off as the weather moderated, but even though the thermostat is set to off, the AC runs. It also looks like the heat does not run. It was chilly last night and I turned the thermostat to heat on and set the temperature appopriately, but no...

Furnace continues to heat past the desired temp. Setting [ 1 Answers ]

I have a gas furnace with an AC unit. My wife wanted to replace the old mercury thermostat with a new digital model. We bought a Honeywell RTH230B. Now the furnace continues to heat, well past the set temperature on the thermostat. I have to switch the thermostat to the off position to get the...

Why the thermostat unable to start the furance [ 1 Answers ]

We have zoned baseboard heat in the house. The thermostat on the bedroom level can not start the furance. In order to get heat for that floor, I first set the temperature at a higher level, then turn on the thermostat in the basement to start the furance. It works like the thermostat in the...

Programmable Thermostat, Fan runs, Heat/Air do not run in Auto setting [ 10 Answers ]

I am installing a Honeywell, RTH230B. My connections are: R to Rh (red jumper to Rc that came with the unit) W to W Y to Y G to G B to nothing The fan comes on (when set to "on").


View more questions Search