    Furnace with smart valve only stays lit for 5 seconds
    Have natural gas hot air furnace with honeywell smart valve SV9520H8067. Unit calls for heat and ignites OK but only stays lit for 5 seconds and goes out. Have had smart valve replaced 5 years ago. Does this sound like another smart valve problem?
    MarkwithaK's Avatar
    MarkwithaK Posts: 955, Reputation: 107
    Senior Member
     
    #2

    Jan 1, 2009, 10:26 AM

    Every Smart Valve is a problem. The symptoms you described could likely be a dirty flame sensor. Normally I would suggest pulling it and cleaning it but with a Smart Valve it can be VERY easy to damage the igniter. If that happens then you are SOL.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Control valve will fire up but will turn off in a few seconds [ 2 Answers ]

I have a heater on my garage and it will fire up but it turns off in a few seconds does that mean that my control valve is bad

Check a concord furnace smart valve? [ 1 Answers ]

How do you check a concord furnace smart valve? Stat is calling. Green light on smart valve is on . But nothing takes place. There is 24 volts to the board on the w. check inducer motor. Its OK . With gas off at the gas cock valve inducer motor running glow coil got on 110 current, so is the smart...

Honeywell Smart Valve failure [ 2 Answers ]

I have a Tempstar furnace and what is happening is the furnace will call for heat and the draft inducer motor will come on and after a momont I will hear the pressure switch go and nothing happens. The electric glow rod does not glow and the furnace does not fire but here is the catch the first...

AC/Heating - smart valve [ 16 Answers ]

We have a home (PA) that only had electric heat when we purchased 7 years ago. Added central air-conditioning. A year later added central propane heating. The heating system "died" a couple of weeks ago. The service company replaced the control board and said it worked. It did not, and they...

Smart valve [ 2 Answers ]

Hello, I have two questions. I have a Tempstar gas furnace that has a intermittent smart valve issue. It sometimes goes days and works fine and others, it will not open the main gas line. I get an orange glow from the ignitor, but the gas never comes on and the cycle ends after a few tries....


View more questions Search