    Thermostat wire gauge
    We've replaced our oil boiler heating system with electric heat pump, and need to add some baseboard heating. Each area will have it's own thermostat. We are using aube TH106 thermostats... "2-wire non-polarized" programmables. The 2 short wires that extend out of the thermostat are black, and multistrand silver wire (aluminum?). We have to run the wires from the heater placement to the place where the thermostat will be mounted on the wall. What gauge wire do we use?

    Thanks in advance.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Dec 7, 2008, 03:21 PM
    The same gauge that is being used to supply voltage to the heaters.

    14 gauge for 15 amp circuit
    12 gauge for a 20 amp circuit
    10 for a 30 amp circuit

    I have no idea what size circuits the heaters require to start with. The thermostat brand and model number means nothing when sizing these circuits unless you overload the thermostat and you will find that out soon enough. Everything has to be matched size wise for the heaters to work correctly. I suggest reading the instructions that came with the heaters to figure out the correct wire size for the heaters and thermostats.
    e-girl's Avatar
    e-girl Posts: 2, Reputation: 1
    New Member
     
    #3

    Dec 7, 2008, 06:41 PM

    Ok, I'm busted, I'm not an electrician. I am only running the wires, a true electrician will do the connections.

    We ran 12-3 w/ground and the heaters are each on their own 20 amp circuit breaker, with a max amp of 8.

    I have one wire run from circuit breaker to position for heater.

    Now I have to run another 12-3 to the thermostat, right?

    Do I have to I have to run a second 12-3 from heater to circuit breaker and to the thermostat, or does the "3" wires in the 12-3 make the circuit?

    This is my first foray into electrical projects, so please be kind.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Dec 7, 2008, 08:07 PM
    Now I have to run another 12-3 to the thermostat, right?

    Yes if you are using metal boxes and or if the thermostat itself requires a ground you need to use 3 wire. Now there is a easier way to do this BUT I am not going to confuse the issue.

    Do I have to I have to run a second 12-3 from heater to circuit breaker and to the thermostat, or does the "3" wires in the 12-3 make the circuit?

    One circuit feed will do for both the thermostat and the heater. The thermostat will basically be a on off switch to control the heater. Usually there is enough space to use the baseboard heater itself as a junction box where it will all come together. OR you could pull the conductors to the thermostat wall box first then make a drop to the baseboard heater. Continue the ground path from main breaker panel to wall box to baseboard heaters or visa versa. All metal areas that need to be grounded have to be grounded correctly. Most if not all of this grounding should be on the manufactures paperwork. They want to make sure the grounding is done so no one gets the shock of there life.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

12 gauge wire to a 15 amp breaker [ 6 Answers ]

I am selling my home and the inspector noted three 15 amp breakers with 12 ga wire. He flagged it as something to be checked by an electrician. Is this an unsafe situation? The buyer is concerned. How much of a concern should this be? If it is not unsafe, what is the explanation for why is...

12 gauge Wire Used w/ 14 gauge Outlet [ 6 Answers ]

Hello, I have a fairly new home I purchased. I am changing my outlets as I am painting the rooms (Laundry Room) and noticed that the previous home owner put in a laundry board (built in) and wired to the nearest outlet on the wall. They used 12 gauge wire to the outlet (from the built in iron...

Failed gass gauge and temperature gauge on 1988 Nissan Pathfinder [ 1 Answers ]

I have a 1988 Nissan Pathfinder 4x4. The gas gauge and the temperature gauge would stop working at the same time when the car warmed up. They both would come back on periodically and then off again. Currently they have not come back on in about 3 months. How do I fix this problem?

What is the cable/wire gauge (product name) for installing 200 Amp Service Entrance [ 1 Answers ]

I am installing a new service entrance to upgrade my home electrical service to 200 amps. 1 Please tell me what gage wire is required from the meter to the weather-head? The service panel with main breaker is inside the laundry room 25 feet from the outdoor meter loop. I will run the...


View more questions Search