    Relays to stop humidification HVAC
    How do I wire a relay in to stop humidification during a call for cooling also how do I wire a cooling system up to a old furnace using a fan centre the old furnace only has a fan limit
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Nov 30, 2008, 01:20 PM

    In both cases: Heatpump or conventional?

    2nd case: one or two speed blower? How is the blower controlled? In the old days, the system was heat only single speed. As part of the upgrade a two speed blower was installed.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #3

    Dec 2, 2008, 06:53 AM
    I believe he is trying to bypass the circuit board and all the safetys. Not good.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #4

    Dec 2, 2008, 12:04 PM

    I'm just wondering if it's one of those relics where you have a summer/winter switch that controls the fan and the motor HP is like 1/3 instead of 1/2 and no G terminal. AC or humidifiers were not even thought of before the time.

    Even this isn't quite enough: How to Install and Wire the Honeywell L4046B combination Furnace Fan Limit Switch Control: a guide to the fan limit switch installation and electrical connections - Honeywell L4064B Combination Fan and Limit Switch

    When a two speed fan is involved.

    In reality, you need to look at:
    1. Is the fan on (Note 1)?
    2. Is there a call for heat?
    Then enable humidifier

    This is tough when there is no low/high speed fan to begin with and it's added.

    Usually there is a third pole that can be used/added on fan centers for EAC's and humidifiers.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #5

    Dec 2, 2008, 01:12 PM

    I forgot about this method as described here:

    http://www.ontimemall.com/aprilaire-...ers-manual.pdf

    You can use a current sensing relay to determine whether the fan is on. It's also easy to determine if in heat mode and fan is on.

    24 VAC Power is between C&W if you have a call for heat, but fan may not be running.

    If you put a current sensing relay on the low speed of the fan combined with the internal humidistat, you should be fine.

    There is lots of little nuances that can cause grief.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

28volt relays [ 9 Answers ]

I have carrier air and heat heating on on heat unit but it has two it has two 28 volt relays that operate the heat strips. One was not working so I purchased another onewith the same ratings but it won't energize. They both say 28 volt dc but when I measured it it has 28volt ac on them. The only...

Cycling and relays [ 2 Answers ]

WHen the temp goes below 35 outside the carrier heat pump cycles every minute. Is this caused by the thermostat or is there a relay to prevent the defrost from cycling at cold temps?

Honda relays [ 1 Answers ]

I have a 93 accord that stops running while driving and won't restart right away .it gives a code 15 so I replaced the distributor and reset the ecu with the back up fuse and it still does it then I found out it could be a relay under left side of the dash. My question is what one is it cause there...

Relays [ 1 Answers ]

Where and what relays do I need to check so I can get some spark. My ingtion fuses are all good so something is telling it not to fire.

Relays [ 1 Answers ]

How do I know if my relay is bad? Replaced the contactor and the unit will run but want come on after it cycles.


View more questions Search