How do I wire a relay in to stop humidification during a call for cooling also how do I wire a cooling system up to a old furnace using a fan centre the old furnace only has a fan limit
![]() |
How do I wire a relay in to stop humidification during a call for cooling also how do I wire a cooling system up to a old furnace using a fan centre the old furnace only has a fan limit
In both cases: Heatpump or conventional?
2nd case: one or two speed blower? How is the blower controlled? In the old days, the system was heat only single speed. As part of the upgrade a two speed blower was installed.
I believe he is trying to bypass the circuit board and all the safetys. Not good.
I'm just wondering if it's one of those relics where you have a summer/winter switch that controls the fan and the motor HP is like 1/3 instead of 1/2 and no G terminal. AC or humidifiers were not even thought of before the time.
Even this isn't quite enough: How to Install and Wire the Honeywell L4046B combination Furnace Fan Limit Switch Control: a guide to the fan limit switch installation and electrical connections - Honeywell L4064B Combination Fan and Limit Switch
When a two speed fan is involved.
In reality, you need to look at:
1. Is the fan on (Note 1)?
2. Is there a call for heat?
Then enable humidifier
This is tough when there is no low/high speed fan to begin with and it's added.
Usually there is a third pole that can be used/added on fan centers for EAC's and humidifiers.
I forgot about this method as described here:
http://www.ontimemall.com/aprilaire-...ers-manual.pdf
You can use a current sensing relay to determine whether the fan is on. It's also easy to determine if in heat mode and fan is on.
24 VAC Power is between C&W if you have a call for heat, but fan may not be running.
If you put a current sensing relay on the low speed of the fan combined with the internal humidistat, you should be fine.
There is lots of little nuances that can cause grief.