Ask Experts Questions for FREE Help !
Ask
    Plann3's Avatar
    Plann3 Posts: 2, Reputation: 1
    New Member
     
    #1

    Nov 24, 2008, 02:32 PM
    Heat pump wire size
    I am installing a 5 ton heat pump. The wire run is 30 feet. The unit specifications are: Voltage 208-230, minimum circuit ampacity 33.0, max breaker 45.0.

    What size supply wire will I need to use?

    Thanks
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Nov 24, 2008, 06:46 PM
    #8cu would be the smallest you could go.
    If you are running NM cable then 8/2NM would be what you want.
    Are you aware of the codes involved with doing such a project?




    Or you could call an electrician. :cool:
    Plann3's Avatar
    Plann3 Posts: 2, Reputation: 1
    New Member
     
    #3

    Nov 26, 2008, 10:48 AM

    Thanks stanfortyman, I went with 6/3 NM just to be on the safe side. I had accessed several web site charts and they had reccommened a range from #3 to #12 (not very helpful). I have a code book but always like to get a second opinion from someone with experience. I wired entire house by myself and try to always do better than code requires.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Nov 26, 2008, 10:53 AM
    You didn't need the 6/3. 6/2 would have been the same thing only you are not wasting a conductor.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Size of wire for a pump? [ 9 Answers ]

I have a submersible pump 1/2 horsepower 425 feet from the breaker box. It is going down hill. What size wire should I run from the box to the pump. What is the best place to purchase the wire (mesquite, Tx), THanks WIll

What size is my heat pump? [ 1 Answers ]

How can you tell how may tons you have on a Rheem heat? I have a Rheem RPNL-042JAZ and was attempting to figure out if I had a 3 ton or a 3.5 ton unit.

Wire New Thermostat to old heat pump [ 1 Answers ]

I am trying to install a Hunter model 44860 thermostat. I have already installed one on the my downstairs gas heating/ac unit, and it works well. I am now trying to get the second one to work on my upstairs unit, an old heat pump with emergency strip heat. This heat pump is an Amana, and is...

How to wire a heat pump & varialble air handler [ 2 Answers ]

Please help how to wire a Goodman 13seer 1.5 ton heat pump and 2.5 ton variable speed air handler to a EWC BMplus 3000 Zoning control system. Thanks, Alo:confused:

Wire colors for heat pump thermostat [ 1 Answers ]

While installing a programmable therostat, two of the indentification stickers fell off the wires. The wires colors are blue and brown and I don't want to hook them up wrong. The "ports" are E and C. Any help would greatly be appreciated. Thanks


View more questions Search