    Size of wire for a pump?
    I have a submersible pump 1/2 horsepower 425 feet from the breaker box. It is going down hill. What size wire should I run from the box to the pump. What is the best place to purchase the wire (mesquite, Tx), THanks WIll
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Oct 15, 2008, 06:40 PM
    What is the actual amperage of the motor, and more importantly what is the voltage?

    If it is 120v you are in for some depressing advice.
    willarrington's Avatar
    willarrington Posts: 42, Reputation: 1
    Junior Member
     
    #3

    Oct 15, 2008, 06:57 PM
    230 v
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Oct 15, 2008, 07:04 PM
    Well, since you don't have the amperage we'll have to assume around 5 amps.

    #12 would be within a reasonable range of voltage drop at 3.25%, but #10 would be better at 2.05%.

    I would go to a real electrical supply house for the wire.

    At this distance, DO NOT share this circuit with anything else. If you must then you absolutely need to go with larger wire.
    willarrington's Avatar
    willarrington Posts: 42, Reputation: 1
    Junior Member
     
    #5

    Oct 16, 2008, 09:01 AM

    So #10 would be ample for that distance
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    Oct 16, 2008, 01:10 PM
    Yes it would.
    willarrington's Avatar
    willarrington Posts: 42, Reputation: 1
    Junior Member
     
    #7

    Oct 16, 2008, 04:17 PM

    It is a 5.5 amp full and a 6.3 amp something else on a 230v submersible pump. It is 440 feet from the breaker box to the pump. Nothing else running off it. I do not know if the increase in amps makes a difference. Thanks for your help.
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #8

    Oct 16, 2008, 04:38 PM

    #10 CU is the way to go!
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #9

    Oct 16, 2008, 04:40 PM
    Are you running your wires in conduit?
    What type of wire are you running?
    willarrington's Avatar
    willarrington Posts: 42, Reputation: 1
    Junior Member
     
    #10

    Oct 16, 2008, 07:33 PM

    Wire that can be buried, 2 wrapped wires and a ground in a sheath

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Vintage stove- 3 wire 220v, what size wire? [ 1 Answers ]

We recently purchased a vintage Crosley range. The old wire was a 3-wire 220v, connected to terminals in the back- the black and red wires were actually 6 or so copper strands, and the white was a silver metal. My question is, what amperage do you think I need? Will 10 be enough? Thanks for your...

Wire Size and panel size [ 6 Answers ]

I have a separate small living quarters that is a single room that is about 180 feet away from the main panel. It is going to get another little bed room a small kitchen and a bathroom also maybe a washer. The main panel is a 100 amp meter socket combo. What should I upsize the main panel to? ...

Wire size etc [ 3 Answers ]

The other day, I read where a supposedly Electrician, could not find the size wire he needed, i.e., # 2 Copper, for, from meter to Fuse panel.. and, this guy told the owner, he could put one or two, of a smaller size, tie them togather to create a larger size wire to carry the heavier load.. the...

Wire size [ 3 Answers ]

What size wire should you use for a 125 amp three phase circuit? How do you figure that for future reference?

4 wire home service entrance wire size [ 1 Answers ]

Mobile home requires 4 wire electrical service entrance wire. Distance is 160 foot from meter to breaker panel. 220V service. What size wire do I use? Can I use diff. size for neutral and ground?


View more questions Search