    Attic Insulation
    I have a full walk through unheated attic with 3 1/2 " of insulation in the rafters.
    I intend to remove the insulation and install approx. R-30 in the floor and cover with
    Plywood to use as storage. In the future I will be heating the space and converting it
    Into a bedroom.
    My question is can I then insulate the rafters and what about the floor insulation MannyR
    KBC's Avatar
    KBC Posts: 2,550, Reputation: 487
    Ultra Member
     
    #2

    Nov 21, 2008, 11:55 AM

    As long as you leave breathable space in the rafters,the roofline must have airflow.

    A product sold at Menards or Home Depot is Styrofoam,conforms to the rafter allowing the insulation to rest against it,but not the roof decking.

    The roof would have condensation with insulation against it,superheated in the summer,and the condensation would begin the rotting of the decking and eventually the rafters.(to say nothing of the shingles)

    Make sure the eaves have open vents and allow the air to pass uninhibited to the peaks.

    Hope this answers your question.

    KBC
    amsteube's Avatar
    amsteube Posts: 75, Reputation: 6
    Junior Member
     
    #3

    Dec 2, 2008, 12:21 PM
    How is the headspace in the attic. Many places will not allow you to have bedrooms in attics. Another thing that you need to check on is the availability of an egress window. Meaning if there is a fire can someone in the attic get out?

    Aaron
    wobblydude's Avatar
    wobblydude Posts: 2, Reputation: 1
    New Member
     
    #4

    Dec 2, 2008, 12:28 PM
    You may have to fur down the rafters to allow enough space for r-30 abot 10" will do
    InspectorDan's Avatar
    InspectorDan Posts: 17, Reputation: 2
    New Member
     
    #5

    Dec 5, 2008, 07:44 AM
    This is a complicated issue and you don't really provide enough information for a full answer.
    I would disregard much of the previous answers Manny.

    First, how are you going to be able to get R-30 into a typical joist channel? You would need to have 2x12 ceiling joists with most insulation materials to achieve that. You want to make sure that you don't over-compress the fiberglass or cellulose insulation in an attempt to reach R-30 since you would be squeezing out the air spaces that make insulation work.

    The possible concern you have with redundant insulation (ceiling and rafters) is that of creating a condensing surface. I don't think that would be an issue in your case as long as you followed good practices in the installation of both insulation materials.

    If you use insulation with a vapor retarder than the vapor retarder should face the living space in a heating climate and should probably face the exterior in a humid cooling climate. Unless you live in a rather extreme heating or cooling climate you may want to avoid using a vapor barrier.

    If you post some photos I will try to be more specific. As a previous replier mentioned you may (but not always) need to keep an air space at the underside of the roof sheathing in the rafter channel. Unvented attics are now allowed by code and can work quite well. Medium or high density spray foam insulation applied to the rafter channels is usually the way to make an unvented attic work without creating a condensing surface.

    Certainteed has a terrific free tutorial on their website that will walk you through correct insulating and ventilating of attic spaces. Try it!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Adding attic insulation [ 4 Answers ]

I am planning on adding 9.5 inches of fiberglass insulation to my attic that has ridge venting with a gable end vent.. . no soffit venting. I plan to lay it over the existing insulation @ 90 degrees. Because there is no soffit venting should I stuff the insulation all the way to the eave or will...

Attic Insulation [ 3 Answers ]

I have a walk out attic over my garage. I was able to install myself r13 batts of over the 3rd car garage area as the studs fit the insulation perfect for what I installed in the walls of the garage. I had extra so used it up. The only section left to insulate is the 2 car part, but am not sure...

Attic Insulation [ 2 Answers ]

I have a two story box house. The attic has insulation under the floor. The 10 ft peak attic is for storage. Should I add insulation under the roof? Thanks, Steve

Attic Insulation [ 5 Answers ]

I'm in the process of building a house and have received conflicting advice on insulating the attic. The architect specified "Sealection" foam insulation against/under the roof with a conditioned attic. However, the builder decided to ignore this specification since that's method is not what they...

Current in my attic insulation [ 5 Answers ]

Okay, this is going to sound weird but I was exploring a space in my attic yesterday and was using my utility lamp. The hook on the lamp brushed up against the metal vent pipe and it sparked and resulted in a burn mark on both the pipe and the lamp hook. Then I brushed up against the attic...


View more questions Search