    Current in my attic insulation
    Okay, this is going to sound weird but I was exploring a space in my attic yesterday and was using my utility lamp. The hook on the lamp brushed up against the metal vent pipe and it sparked and resulted in a burn mark on both the pipe and the lamp hook. Then I brushed up against the attic insulation (it has that metallic paper covering) and that sent an electric current spark as well. The metal drain pipe and the metallic insulation do rub against each other. The lamp is not doing this in other locations in the house. And when I touch the insulation or pipe without the utility light nothing is occurring (I had done this beforehand as I had done many times over the years and not after the sparking incident). So I am wondering do I have a wiring problem somewhere in the walls of my home that is sending a current into the vent pipe? What's going on?
    pelle's Avatar
    pelle Posts: 96, Reputation: 0
    Junior Member
     
    #2

    Nov 25, 2007, 02:45 PM
    There are a number of things that could be happening..
    1. The outlet that you are using for the utility light is defective and it is putting voltage on the case ground..
    3. There is a problem with the wiring internal to the utility light and by chance it only happened in the attic.
    3. You could have a bad utility neutral and this is putting voltage on you water pipe ground which could be going onto all the pipes in the house .
    4. You could have stray voltage from a well pump, electric fence or even from a neighbor and this is coming in through your driven grounds.
    Since this is not happen all over the house I would suspect 1 or 2.

    Get a extension cord and plug it into another outlet in the house and bring it the outlet in question.. Use the ground on this cord and check each of the holes on the outlet in questions with a electric tester.. you should only get voltage from 1 hole to ground.. the longer one and the round one should show no voltage..

    Let us know how you make out and I am sure tk will have more info and suggestions..
    PSpadafora's Avatar
    PSpadafora Posts: 3, Reputation: 1
    New Member
     
    #3

    Nov 25, 2007, 03:21 PM
    Thanks. I'm pretty sure the outlet is okay. It's grounded correctly (I used a tester) and only reads voltage from short slot-ground hole connection. The utility neutral on the water heater looks to be intact as well; it's a new water heater and I can see the cold water-hot water ground connection clearly.
    As for the utility light being defective, I tested in the basement (no problems) then returned and recreated the sparking incident in the attic. Conclusion: I think it's okay as well.
    I suspect there is a frayed wire somewhere in my wall (not visible from my inspection) that's grounding to the metal vent pipe. While I have a volt meter, I really don't know how to use it to test the pipe.
    pelle's Avatar
    pelle Posts: 96, Reputation: 0
    Junior Member
     
    #4

    Nov 25, 2007, 03:33 PM
    Use the an extension cord pluged into a grounded outlet and use the tester from the vent pipe to the ground on the cord.. this will read any voltage on the pipe..
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #5

    Nov 25, 2007, 03:53 PM
    When I worked in a paint factory, we had a lot of bronze tools. This was not because I go back to the bronze age. Steel against steel causes sparks. Try the vent pipe with the light unplugged.

    Whatever the cause, you need to find it.
    biggsie's Avatar
    biggsie Posts: 1,267, Reputation: 125
    Ultra Member
     
    #6

    Nov 25, 2007, 04:00 PM
    I believe you need to test the light with an ohm meter

    Test from the lamp shield to each of the plugs

    I believe there is a short in the light to the reflector

    Depending on way it is plugged in will cause a spark

    If you plug it in one way it sparks -- But if you unplug it

    And turn the plug 180 degrees it will not spark

    The reason is now the neutral is shorted -- no spark to ground

    The foil back on insulation was probably grounding to something

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

"A" frame attic insulation and venting [ 4 Answers ]

I am converting my "A" frame attic into a living space. The joists stick out 5" from the roof and are 22" apart. It's an old house and measurements change give or take a half inch from joist to joist. Even though there is no ridge vent there are roof louvers about 3 ' from the peak. I can only...

Current ratio and non current assets [ 1 Answers ]

How do I know what each makes contains. current assets 25,000 liabilities 40,000 equity 55,000 non current assets=80,000 ( Is this correct) non current 60,000

Current & Non-Current Assets [ 3 Answers ]

Why is classification of Assets into Current & Non-Current necessary? Or not necessary?

Adding attic insulation [ 5 Answers ]

I recently bought a house and want to add insulation to the attic, the existing insulation has the vapor barrier facing down to the sheetrock and there is a section where it appears that there is a silver aluminum vapor facing up. My question is If I want to add at least 3" of insulation what type...

Putting plywood over attic insulation. [ 2 Answers ]

We have an attached garage that is not heated. In the attic I am planning to put some cellulose insulation over the fiberglass stuff. Once this is done I would like to put some plywood down so we can store stuff up there. Should I leave small spaces between the plywood to keep condensation from...


View more questions Search