    Furnace Kicks on But Doesn't Move Air
    I have a natural gas furnace that will kick on and I can hear the burners light, but it will not cirrculate the air ( I can turn the fan on using my thermostat) Any Ideas on what I need to do? Thanks in advance
    npb575s's Avatar
    npb575s Posts: 19, Reputation: 1
    New Member
     
    #2

    Nov 16, 2008, 08:30 PM
    After reading some more posts I found that the error code that this heater has is an ignition failure, I can see the heating element heat up and the system tries this three times and then gives me this error. What would be my next troubleshooting task? Thanks again for any help.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #3

    Nov 16, 2008, 10:47 PM
    Brand of unit?
    Exact Model number of unit?
    npb575s's Avatar
    npb575s Posts: 19, Reputation: 1
    New Member
     
    #4

    Nov 17, 2008, 06:49 AM
    There isn't a model or brandname on this system, I just bought this house in may, the only other thing that I do know is its an 80+ system. Sorry and thanks.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Nov 17, 2008, 03:09 PM
    Since no info is available the best guess would be a defective fan and limit control OR the control that activates the blower in the heat mode. There can be various types of switches that can accomplish this and in some units the circuit board controls the blower also.
    npb575s's Avatar
    npb575s Posts: 19, Reputation: 1
    New Member
     
    #6

    Nov 17, 2008, 07:58 PM
    Shouldn't the furnace still light the gas even if the blower doesn't kick on? When I turn the fan on my thermostat to on the blower does kick on. Is it possible that it is the gas valve?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #7

    Nov 17, 2008, 10:53 PM
    From your first post!

    I have a natural gas furnace that will kick on and I can hear the burners light, but it will not cirrculate the air

    Now you say

    Shouldnt the furnace still light the gas even if the blower doesnt kick on?

    I am confused by your posts.
    npb575s's Avatar
    npb575s Posts: 19, Reputation: 1
    New Member
     
    #8

    Nov 18, 2008, 06:49 AM
    Sorry about that, The burners do not light. Thanks for all the info too.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #9

    Nov 18, 2008, 07:08 AM
    Problems of this nature can be brand and model specific. By law there has to be a model number and brand name on the equipment. Otherwise it is just a very bad guessing game.
    letmetellu's Avatar
    letmetellu Posts: 3,151, Reputation: 317
    Ultra Member
     
    #10

    Nov 18, 2008, 10:30 AM

    I think the problem is the flame sensor So hvac1000 why don't you advise him on how to handle this problem, if you agree that it might be the flame sensor.
    npb575s's Avatar
    npb575s Posts: 19, Reputation: 1
    New Member
     
    #11

    Nov 18, 2008, 11:46 AM
    Quote Originally Posted by letmetellu View Post
    I think the problem is the flame sensor So hvac1000 why don't you advise him on how to handle this problem, if you agree that it might be the flame sensor.
    If that is correct, I think that I see were its located, and if I'm not mistaken from the other posts on this site I need to pull it out and clean it with steel wool or copper wool. I am also trying to get someone to come and look at it, if I can't resolve it with your guys help. Thanks again to all that are helping.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #12

    Nov 18, 2008, 12:43 PM
    Sounds like he has a handle on the flame sensor cleaning.
    npb575s's Avatar
    npb575s Posts: 19, Reputation: 1
    New Member
     
    #13

    Nov 18, 2008, 05:15 PM
    Problem found by HVAC Tech. the upper limit switch. But he didn't have one. Are these made to trip by a certain temp? Is it possible to swap the upper and lower temp? There again I am no expert to HVAC. Thanks for all the great advice.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #14

    Nov 18, 2008, 05:19 PM
    Are these made to trip by a certain temp?

    Yes

    Is it possible to swap the upper and lower temp

    NO do not try and swap. The one that is out is a safety device.

    These parts are available. What are all the part numbers on the switch and the temp numbers. Also give a description.
    npb575s's Avatar
    npb575s Posts: 19, Reputation: 1
    New Member
     
    #15

    Nov 18, 2008, 05:33 PM
    Quote Originally Posted by hvac1000 View Post
    Are these made to trip by a certain temp?

    Yes

    Is it possible to swap the upper and lower temp

    NO do not try and swap. The one that is out is a safety device.

    These parts are available. What are all the part numbers on the switch and the temp numbers. Also give a description.
    Thank you very much for your help. I have found the part and ordered it from a online vendor the total cost was about 16.50. Again thanks to all that have helped.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #16

    Nov 18, 2008, 05:43 PM

    Strange, usually when the high limit trips, it will cause the blower to come on, but you say the blower will never come on unless you turn it on at the stat? I do believe we will be hearing more about your problem.
    npb575s's Avatar
    npb575s Posts: 19, Reputation: 1
    New Member
     
    #17

    Nov 18, 2008, 06:01 PM
    What other problems do you think that I might have? The part I'm replacing is a goodman
    b1370154.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #18

    Nov 18, 2008, 06:11 PM
    That is a roll out switch it is a safety device. If the new one trips you have another problem.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #19

    Nov 18, 2008, 06:14 PM

    Does the flame ever actually come on at all, even for a few seconds? Or do you get no flame ever.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #20

    Nov 18, 2008, 06:28 PM
    Its hard to tell what the tech meant by upper limit. I would think he meant high limit. Could have meant rollout switch. Could be a limit on the blower squirall cage. I guess, for the cheap part advised by the tech, I would start there, hope it takes care of your problems. Just let us know how it turns out.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Coleman Furnace blower kicks on and off [ 3 Answers ]

I have a Coleman model DGAT070BDE that is 9 years old. It has suddenly started acting strange. The blower motor will kick on and run for about a minute, then shut off for about 5 minutes and start all over again until I shut off the power to the furnace. The thermostat is not calling for heat as it...

Furnace kicks in for 5 seconds- shuts off [ 1 Answers ]

My furnace kicks in and shuts off within seconds. Sometimes it does this several time in a row. Sometimes runs perfectly normal. Thermostat fluctuates by 3 degrees as I'm standing there looking at it. Any ideas?

AC & Electric Furnace kicks in same time [ 1 Answers ]

Hello, I have thermostat set at 75F for COOL, but the heater in Train electric furnace unit also kicking at the same time. I have replaced 90343 Relay but no help. Please advise the poor man:confused:

Heater kicks on but doesn't blow or stay on [ 1 Answers ]

Heater doesn't kick on below 70 degrees. When it does kick on with thermostat set higher than 70 it will turn on run and then blow. (Pilot light works) Doesn't blow as long as it should then shuts off and idles (runs) again. Had a certified furnace repair person look at it. The limit switch was...

Furnace Gas Kicks Off [ 2 Answers ]

Im going to follow the "please answer" before I ask here. Manufacturer: Goodman (installed new in 2002) Efficiency: Natural draft, Type of system: Forced air


View more questions Search