    Furnace snuffing system
    Dear Gen;

    We are reviewing the future requirements in terms of applicable fire fighting system in the hot oil furnace.

    The required calculated quantity of N2 within the protected space (radiant & convection zones) is 766 m3
    What is the number of N2 cylinders equivalent to the 766 m3 ? Considering that cylinder shall be pressurized to 300 bars


    Best Rgards
    K.Dabeski
    robkelly2242's Avatar
    robkelly2242 Posts: 57, Reputation: 0
    Junior Member
     
    #2

    Nov 12, 2008, 12:03 AM
    At 300 bars you need approx. 2.6 meters^3 of compressed N2. If your standard gas cylinder has .04M^3 volume, you need about 65 cylinders.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search


Check out some similar questions!

Furnace codes--system lockout /check line clarity? [ 2 Answers ]

Our furnace is only blowing cold air and the blower will not shut off with the thermostat. The indicator light flashes 2 times-and the code thing says it means system lockout -check line clarity.:confused: The ignitors try to light but go out right away. Now it is flashing constantly meaning...

Converting forced hot air system to baseboard heating system [ 1 Answers ]

When considering converting from forced hot air to baseboard heat, is it possible to just add piping / water boiler / baseboards and do nothing with the forced hot air system (use it for AC) ?

Transferring Brinks Alarm System to Non-Monitored System [ 5 Answers ]

I understand that when you cancel your Brinks-monitored security system that they come and remove their equipment (which you apparently don't own) or you can buy all their equipment for $500. The equipment removal exposes unpainted walls and previously-covered holes. Is it possible to install a...

Furnace. Forced Hot Air System [ 1 Answers ]

My furnace is making a scratchy noise, almost like there is a metallic wire scratching the inside of the furnace. It is not a rattling sound and this is not its normal noise. It seems to be making it even when the heating or the domestic hot water systems are not calling for hot water. In other...

How do I increase H2O pressure on well system with a water filtration system? [ 2 Answers ]

Howdy, I would like to know how I can increase my water pressure. My current system uses a well pump with a small pressure tank, and "D" control valve. It then runs through a WATERSOFT filtration tank, RAINSOFT water softner, and on the Hot water side, an AQUASTAR on demand hot water system. I...


View more questions Search