    Adjust Steam Boiler Water
    I have an old Peerless steam boiler in the hose I've been living in for the last 5 years. I have made improvements to the unit as the technicians who service it recommended periodically. At the end of last winter, they had me relace the low water cutoff. The boiler was asking for too much water and they said the "float" in the old water cutoff was shot. It was a few hundred buck to buy and replace it. I just turned my heat on for the first time yesterday. After 2 hours running, radiators started leaking and I could hear boiling water in them as well. There were some banging noises too. I shut the heat. This morning I checked the glass water level indicator and it's filled to the top rather than half - where I was always told it should be. Any ideas?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Oct 20, 2008, 10:58 AM
    The fill glass on a steam boiler is never to the top because the boiler needs head room to create steam. You probably have a problem with the boiler fill valve allowing too much water into the boiler.

    NOTE: if you do not know what you are doing with a steam boiler call a pro for a on site inspection and repair. To dangerous to play with.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Replacing a steam boiler site glass [ 4 Answers ]

How do you replace a steam boiler site glass that cannot be seen through.

Skimming my steam boiler? [ 7 Answers ]

I moved into my house three years ago, and one of the first things I did is change out the old steam boiler, that was fueled with oil remove the oil tank, and then replace it with a new gas fired boiler, and Wow what a difference. The new boiler is a Weil-Mclain packaged boiler, model EG, series...

Water Hammer on Hot water loop of Steam Boiler System [ 3 Answers ]

We have a steam boiler that provides steam for most of the house but also has a hot water loop for the additions. We have been getting a lot of water hammer and it sounds as if it is coming from the area where the first hot water radiator starts (ie it is from the hot water loop). Does anyone...

Weekly Flushing of a steam boiler furnace [ 1 Answers ]

I just bought a house that has steam radiator heat and the boiler system says that it should be "flushed" weekly during the heating system. Do you know how to do this?


View more questions Search