Hello:
I have a Armstrong Air Ultra 5 Tex80 Furnace HoneyWell Gas Valve SV9520H8034
Ultra V Tech 80 Armstrong Air Mack GIN80AT075D12A-1 Serial #1602L21430
It has a smartVlave on it as well.
I can't get it to start. The thermostats has been changed on it and I have jumped out R and W on the control Panel board to see if the blower on top of the smart ysytem would start, Nothing / I have 24 volts to the control baord and the A/C works fine Just can't get the fan blower or whatever you call it on top of Smart Valve to start which I believe cleans out the chamber of any fumes.
I Hooked up 110 volts to the fan Blower to see it it works and it does ! I would be mostly grateful if someone can help me here with this Driving me crazy
Terry:confused:
|
|
 |
Heating & Air Conditioning Expert
|
|
Oct 3, 2008, 01:32 PM
|
|
There have been many problems with the smart valve especially at the connections. Call for ON SITE SERVICE for your unit so you do not cause any further damage or get hurt in the process.
|
|
 |
New Member
|
|
Oct 3, 2008, 02:41 PM
|
|
Comment on hvac1000's post
He must be in the business That's why he asked that way. I am knowledgeable on electric Just wanted help, not phrases
|
|
 |
Plumbing Expert
|
|
Oct 3, 2008, 07:20 PM
|
|
If you jumped rw and nothing happened, and you put 120 straight to the blower and it worked, I would think your control board was bad. Is there anything between your blower and board (wiring wise?)
|
|
 |
New Member
|
|
Oct 3, 2008, 07:31 PM
|
|
[QUOTE=mygirlsdad77;1304493]if you jumped rw and nothing happened, and you put 120 straight to the blower and it worked, I would think your control board was bad. Is there anything between your blower and board (wiring wise?)[/QUOTE
I checked the voltage to the Smartvalve and there was voltage can't remember what it was ! But the smartvalve has 3 connections on it plugin's that is. The blower wires go into the Samrtvalve blue cover I have voltage on the control board in fact the A/C is workign fine off the control board I got voltage 24 volts on the letter ( R ) So I jumped it from are to w But nothing when on . Could it be the samrtvalve Just asking
Thanks so much for helping me Wish I could send you a picture of it I have ONE too
|
|
 |
Heating & Air Conditioning Expert
|
|
Oct 3, 2008, 09:21 PM
|
|
Could it be the samrtvalve Just asking
Yes
They are trouble prone especially the connections.
|
|
 |
New Member
|
|
Oct 4, 2008, 09:04 AM
|
|
Ok HVAC guy
Thank you for your answer. If the smartvalve wasnt' so expensive I would change both (SMARTVALVE and the control board.
This is my last question if you can answer it If you jump out the ( R and W) what should come on the INDUCTION BLOWER. Cause I did that and nothing happened But If I jump out the (R and W) I get the A/c to work. That part of the Heating and A/C are workign fine through the thermostat THANK GOD! But nothing to the heat. If jumping out the (R and W) don't work wouldnt' thatbe the control board Cause if the control board isn't workign It can't send a signal to the smartvalve right
Just asking You know more about this then I do and I am just trying to fix it and alos I live like 37 miles one way to any store. And here in Oklahoma You can't seem to find a dealer for this burner Armstrong Air Ultra 5 Tex 80. So anythign you give me is a plus AMEN
Thanks again !
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Furnace won't keep running
[ 9 Answers ]
I have a programmable thermostat. In the morning when the furnace comes on it will run for one cycle and then stop. In order to get it to start again, I have to turn off the heat and then turn it back on again. I have had technicians out several times. They have replaced various parts and...
Furnace running when everything off
[ 3 Answers ]
I have a colman 7900 series in a mobile home dated 1985 just purchased in Oct 07. The problem is the weather has been warm so shut furnnace off and noticed today the fan is running automatic, I do not want this as to save on electric bill... Do I have a problem and where does the switch need to be...
Knocking in Furnace While Running
[ 1 Answers ]
When the furnace kicks in and is running I can now hear a knock every 4 or 5 seconds that appears to be coming from inside the furnace. What could it be? When it stops running the knock stops. It doesn't happen when the blower is on by itself.
Gas furnace pilot trouble. Goes out while furnace is running!
[ 1 Answers ]
About a month ago I put in a new thermocoupler in my furnce and it's been working fine. This morning I woke up to no heat. I can re-light the pilot with no problems. The piot light keeps on burning if I don't turn the thermostat up to turn on the furnace. Then when I set the thermostat to 70...
Oil ran out; we refilled, but now we can't get furnace running again
[ 1 Answers ]
We woke up the other morning to our house being 53 degrees. We knew we were getting low on oil, but hadn't realized *how* low. We got some oil delivered that day, but we can't seem to get the thing running again. It's an old --very old-- Thermopride furnace. My dh has pressed every button he can...