    Can I replace a 15-amp breaker w/a 20-amp?
    Newb question -

    My home is less than 2 years old. I'm not sure which gauge wire it is wired with (14 or 12). I have 3 upstairs rooms all on one 15-amp breaker. Both of my kids rooms and our workout room. My wife has a tanning bed (120v, 15a) in the workout room. Sometimes, the breaker trips when she turns on the bed but not all of the time.

    My question is: is it SAFE to upgrade to a 20-Amp breaker?

    Keep in mind that the tanning bed is only on for 7 minutes at a time (maximum time, timer driven) and she is always present when it's on. (basically, it doesn't draw any power until she's laid down inside of it).

    My concern is excessive heat from the amperage draw degrading the wire over time and possibly causing issues in any of the 3 rooms.

    Thanks,
    Thom - New Mexico
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Oct 1, 2008, 07:40 AM

    The short answer is no. The breaker trips when the amperage draw is greater than 15 amps. To permit more than 15 amps would cause the wire to over heat and create a fire hazard. Your wife will have to insure that nothing else on that circuit is being used when she is using the tanning bed. It's either that or run a new 20 amp circuit.
    ooomph's Avatar
    ooomph Posts: 2, Reputation: 1
    New Member
     
    #3

    Oct 1, 2008, 08:13 AM

    Thanks Harold:cool: for the quick response! I might just have a pro come out and wire her a dedicated 20amp breaker outlet solely for her tanning bed. Good thing is that the room in question is directly over the garage and breaker box. Thanks again Harold.

    Thom - New Mexico :)
    ceilingfanrepair's Avatar
    ceilingfanrepair Posts: 5,733, Reputation: 109
    Uber Member
     
    #4

    Oct 1, 2008, 05:51 PM

    Check and see if the wire is 12 or 14 gauge.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #5

    Oct 2, 2008, 04:30 AM

    Hopefully the electrician will remove panel cover, determine if it is #12, then it can go on a 20 Amp breaker, as well as check if all rooms and tanning bed are wirenutted, then connected to 1 breaker, May be able to separate and add breakers.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How do I replace a 30 amp breaker with a 20 amp breaker? Must I replace the wiring? [ 15 Answers ]

I have purchased a GE built-in oven to replace the 60 year old oven that was installed when the house was built. The original oven uses a 30 amp breaker. The salesperson told me I must change the breaker to a 20 amp to accommodate the new oven, but he's unsure whether the wiring must be changed as...

How do I safely replace circuit breaker? [ 3 Answers ]

In my garage I have two separate overhead light bulb sockets, each is connected to a separate wall switch. One works, the other does not. Using a tester, there is no power at the socket that is not working. I have replaced the wall switch and the fixture, it still does not work. The last thing...

Replacing GFCI Breaker With A Regular Breaker [ 1 Answers ]

I have a 15 amp circuit serving only a single outlet on my deck. It is protected by a GFCI circuit breaker in the home's single 125 amp service panel. I wish to replace the GFCI breaker with a regular 15 amp GE breaker. I will then protect the circuit with a GFCI outlet. I am familiar with...

New 15A breaker trips main 100A breaker [ 6 Answers ]

Hi, I've been finishing my basement and I added a few 15A breakers One room has 8 outlets in series with the first starting about 6 feet from the main panel. There is currently no load on this outlets. When installing the drywall I accidentally shorted the outlet closest to the panel. It...

Replacing a circuit breaker with a GFI breaker- q on neutrals [ 1 Answers ]

In process on installing withquestion on neutral wires. Do you take the neutrals out of the in the main panel neutral and put them in into the breaker where its labelled "load neutral terminal" and only have the neutral "pig tail" to the panel neutral bar? Thanks!


View more questions Search