Basement bathroom Layout
I am thinking of moving the basement laundry room and putting in a new bathroom. From reading all of the posts, I think I have a decent handle on what needs to be done. I have attached my proposed layout.
Are there any problems with this?
My one concern is the floor drain. I need some way to drain water in case something happens to my HW heater per the local inspector. I could use a pan and pump for this, but its located 30' plus feet away and don't really want to run the pvc pipe.
I do have a 3/4" drain line for the condensation for the AC, would this line be large enough if I tapped into it? If not, how large should the drain pipe be for the indirect drain if I chose this way?
|
|
 |
Eternal Plumber
|
|
Sep 10, 2008, 11:30 AM
|
|
Hey Nate,
Check with your local Building Department about wet vents and using AAV's. I would much rather see a vent through the roof here.l
I do have a 3/4" drain line for the condensation for the AC, would this line be large enough if I tapped into it?
3/4" Pvc is what we use on heater pan drain lines. If you can't put bit of slope on the pan drain I'm afraid that the AC condensate will drain into the heater pan. You could install 3/4" check valve on the pan drain and be safe that way also. Good luck, Tom
|
|
 |
Home Repair & Remodeling Expert
|
|
Sep 10, 2008, 11:43 AM
|
|
If you are busting up the floor anyway I'd suggest that you make your washer stand pipe and drain line 3" which is what the 2009 code calls for. I'd also ask that inspector what he thinks about a HW pan with a condensate pump connected to it. Last but not least do you have a reason for running separate drain lines for the washer and the laundry tub, they can both be on that one new 3" pipe.
|
|
 |
Junior Member
|
|
Sep 10, 2008, 12:21 PM
|
|
There is only one drain line for washer and laundry sink. The other line is for the floor drain (if I use one). Could the floor drain come off from the washer line. I will upgrade the washer/laundry sink line to 3".
If I tapped the heater pan line into the AC condesation line, I was assuming I would be using a pump and therefore tie into the AC line from above.
[QUOTE=speedball1]Hey Nate,
Check with your local Building Department about wet vents and using AAV's. I would much rather see a vent through the roof here.l
I would too but I do not have any easy way to get to the attic. I am going to try to set at least the vanity sink vent up so that I can remove the AAV and run into the attic when I redo the bathroom up above
One more thing, if the washer laundry sink line is 3", should I keep 4" from the main past all the wyes then reduce to 3" before the toilet?
|
|
 |
Home Repair & Remodeling Expert
|
|
Sep 10, 2008, 12:36 PM
|
|
That's more of a rough in question up Tom's alley but I think 3" all the way to the main is fine, what do you think Tom?
|
|
 |
Eternal Plumber
|
|
Sep 10, 2008, 03:16 PM
|
|
I would run 4" all the way to the toilet, 3" from the laundry tray and washer and 2" from the lavatory. Good luck. Tom
|
|
 |
Home Repair & Remodeling Expert
|
|
Sep 10, 2008, 03:53 PM
|
|
So there you have it, from a professional plumber who has done rough ins for many years. Glad to see Tom recommends a 3" from the laundry tub.
|
|
 |
Junior Member
|
|
Sep 11, 2008, 06:01 AM
|
|
Thanks for the great help.
One last question
There is only one drain line for washer and laundry sink. The other line is for the floor drain (if I use one). Could the floor drain come off from the washer line or should it tie into the 4" line running to the toilet.
|
|
 |
Eternal Plumber
|
|
Sep 11, 2008, 06:29 AM
|
|
 Originally Posted by nate220
Thanks for the great help.
One last question
There is only one drain line for washer and laundry sink. The other line is for the floor drain (if I use one). Could the floor drain come off from the washer line or should it tie into the 4" line running to the toilet.
I would connect the floor drain to the toilet branch. Less chance of a back up there because the toilet discharges by gravity while the washer discharges under great force. If the floor drain was on the washer line that would make it the lowest fixture and more subject to backups. Good luck, Tom
|
|
 |
Junior Member
|
|
Sep 19, 2008, 01:01 PM
|
|
I was thinking of just putting in a floor drain and eliminating the washer stand pipe, this would mimic my current situation. I would drain the laundry sink into the floor drain and the washer into the laundry sink. Are there any problems with this?
If I did this, can the floor drain be 3" or should it be 4".
If I kept the washer standpipe and drained the laundry sink into that line, should I be worried about the water in floor drain's trap evaporating since nothing is draining to it?
|
|
 |
Eternal Plumber
|
|
Sep 20, 2008, 07:41 AM
|
|
I was thinking of just putting in a floor drain and eliminating the washer stand pipe, this would mimic my current situation. I would drain the laundry sink into the floor drain and the washer into the laundry sink. Are there any problems with this?
If I did this, can the floor drain be 3" or should it be 4".
This is called a indirect waste and will be acceptable. I would make the floor drain 3 inch.
If I kept the washer standpipe and drained the laundry sink into that line, should I be worried about the water in floor drain's trap evaporating since nothing is draining to it?
Youb can cap off the washer stand pipe or pour a quart of cooking oil down the stand pipe and forget about evaporation. Good luck, Tom
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Basement bathroom layout
[ 6 Answers ]
Our unfinished basement has rough-ins for a toilet, sink and shower. I'm trying to determine if a small, 32 sq ft bathroom will be adequate or if the layout is too small. I could enlarge the space but the plumbing rough-ins really limit the "business" space in the room.
I've uploaded digital...
Basement Bathroom Layout
[ 1 Answers ]
Hello,
I've attached the rough-in layout of my basement bathroom. Fortunately, I had pictures while the house was being built so I know the layout of plumbing underneath the slab. I've indicated these drain lines as well. Hopefully the picture and my probable misuse of terms in this email all...
DWV Layout in Basement
[ 25 Answers ]
I am reposting since my original already moved to the 3rd page
Any help with the layout would be helpful. I would like to start tearing up the concrete this weekend if I can get this figured out.
I would like to put in a bathroom in my basement and move the laundry area. The existing laundry si...
Basement Layout
[ 3 Answers ]
Can you all please look this over. We are just about ready to go with this project. I have just cut all of the concrete. Dug the hole for the sewage basin and I am now just wanting a review on this before I begin. This has been one long day of digging and cutting.