    Subpanel 130' run grounding
    Hi,
    I ran a subpanel aprox 130' from my main panel out to my shop and would like clarification on weather the ground rod at the sub panel should be bonded to the neutral.

    Thanks
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Sep 9, 2008, 11:58 PM
    No.

    Ground and neutral should be isolated at the sub-panels. You usually have to buy a ground bar kit and not install the neutral to ground bonding screw.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Sep 10, 2008, 03:50 AM
    Actually it depends on what you ran for a feeder.

    Under certain circumstances, a "3-wire" feeder IS/was allowed. In this case the neutral IS bonded to the panel and also serves as the ground, just like in a main service panel.

    A ground rod (or two) is always required at a remote structure sub-panel.

    What did you run for a feeder?
    Highway162's Avatar
    Highway162 Posts: 2, Reputation: 1
    New Member
     
    #4

    Sep 10, 2008, 08:02 AM
    Hi, Thanks for the quick response guys!

    I ran 3 #4 (copper)

    Do I need to run a ground wire from panel to panel ?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

200 amp panel feeding a 100 amp panel roughly 130' away [ 7 Answers ]

Hi all, We are building a apartment above the garage,my question is what size wire do I need to run from the 200 amp panel to the 100 amp panel roughly 130' away? I want to use aluminum wire as I think copper would be to costly. Thanks for your help in advance, Dude :eek:

Subpanel grounding [ 2 Answers ]

TK - Stan - Wash - KISS, For the purpose of discussion: :) A subpanel located in the same residence as the main panel uses the main panel's Ground system. Separate Grounding rods and EGC are not needed for the subpanel For a remote building, a sub panel must have its own independent...

Subpanel Grounding Rods and Neutral Bar [ 7 Answers ]

My main service panel is installed in a detached garage. Our new home is fed by a subpanel run underground from the garage. At the garage panel I have two ground rods and the neutral bar and ground bar in the panel are connected. At the house subpanel location do I need additional ground rods...

Dose a newly added subpanel need a grounding rod? [ 5 Answers ]

I'm goining to add a new subpanel to a detached garage , for a 6-3g 240v outlet for use with mechanic's tools (small mechanic work) and a few 120v outlets and mabe a over head light (florecent) Now I've studied the panel info I've found online but haven't came across the QUESTION of Do I need to...

Grounding a subpanel [ 1 Answers ]

I have a set of direct current solar panels mounted on a metal structure (carport). All the panels and the structure are grounded to a ground rod driven near one of the support posts. Can I use the same ground rod for the ground connection of an alternating current subpanel mounted on one of...


View more questions Search