    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #1

    Jun 18, 2008, 03:28 PM
    Subpanel grounding
    TK - Stan - Wash - KISS,

    For the purpose of discussion: :)

    A subpanel located in the same residence as the main panel uses the main panel's Ground system. Separate Grounding rods and EGC are not needed for the subpanel

    For a remote building, a sub panel must have its own independent grounding system that is not connected to the Main Panel grounding.
    </IMG>
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Jun 18, 2008, 04:01 PM
    Almost:

    Neutral to ground rod bonding occurs at the utility disconnect.

    If disconnect is separate/remote such as at the meter base, all panels are treated as sub-panels.

    If a sub is installed in a detached structure, both a ground to the main panel and a ground rod is installed, otherwise just a ground.

    At the sub ground and neutral are isolated.

    Why a ground rod for a detached structure?

    1. To handle lightning strikes, otherwise it could travel along the feeder.
    2. Surface ground potential can be different during storms. Distance can increase this difference. That bond can help equalize the earth's potential.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Jun 18, 2008, 07:02 PM
    Quote Originally Posted by donf
    For a remote building, a sub panel must have its own independent grounding system that is not connected to the Main Panel grounding.
    Not so Don. There is no wording making an independent rod mandatory.



    Here is the NEC text on this:

    250.32 Buildings or Structures Supplied by Feeder(s) or Branch Circuit(s)

    (A) Grounding Electrode Building(s) or structure(s) supplied by feeder(s) or branch circuit(s) shall have a grounding electrode or grounding electrode system installed in accordance with 250.50. The grounding electrode conductor(s) shall be connected in accordance with 250.32(B) or (C). Where there is no existing grounding electrode, the grounding electrode(s) required in 250.50 shall be installed.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Subpanel Grounding Rods and Neutral Bar [ 7 Answers ]

My main service panel is installed in a detached garage. Our new home is fed by a subpanel run underground from the garage. At the garage panel I have two ground rods and the neutral bar and ground bar in the panel are connected. At the house subpanel location do I need additional ground rods...

Hot tub grounding bar [ 9 Answers ]

I got a free hot tub... yeah right free-the 6/3 wire itself is going to run $300! Anyway, the instruction manual calls for a 50 amp breaker and the 6/3 UF wire with ground. It also calls for a #6 copper wire that is attached to a grounding bar that is to be buried. I have heard two solutions,...

Grounding a GFI [ 1 Answers ]

I am using an existing wire that was used for a dryer. I have changed the breakers to 2-20 amp single pole breakers and am splitting the line to make two 110volt GFI outlets for a whirlpool tub (1 for pump and 1 for heater). I have a red, white, and black wires, however, there is no bare copper...

Dose a newly added subpanel need a grounding rod? [ 5 Answers ]

I'm goining to add a new subpanel to a detached garage , for a 6-3g 240v outlet for use with mechanic's tools (small mechanic work) and a few 120v outlets and mabe a over head light (florecent) Now I've studied the panel info I've found online but haven't came across the QUESTION of Do I need to...

Grounding a subpanel [ 1 Answers ]