    Service to garage without remote disconnect
    Service to detached garage : starting at newly installed meter adjacent to existing house meter,3 2/0 copper conductors through 2" pvc conduit underground, to 200 AMP interior distribution panel in garage, approx. 60' run. Ground rod and #6 copper solid, adjacent to garage panel, same ground set-up at meter, plus grounded to house copper plumbing. Garage plumbing is all plastic. My question; with the above set-up does the neutral and ground in the garage panel stay bonded together. This is how the electrician did it, explaining that having/ not having disconnect at meter determines neutral/ ground bond. Does this sound correct? He energized it to check it, then blocked meter connection at socket to safe it till I call utility to initiate service.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Sep 6, 2008, 05:55 AM
    If he is going right from the meter to the garage then there is NO place to even land a separate equipment ground. A 3-wire lateral is all that is run, just like to your house.

    So you are saying the garage has it's own meter?
    561packrat's Avatar
    561packrat Posts: 80, Reputation: 1
    Junior Member
     
    #3

    Sep 6, 2008, 11:03 AM
    Quote Originally Posted by stanfortyman
    If he is going right from the meter to the garage then there is NO place to even land a separate equipment ground. A 3-wire lateral is all that is run, just like to your house.

    So you are saying the garage has it's own meter?
    Yes it has it's own meter. Present goal is to use space as art studio, possibly in the future converting into efficiency apt.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Clarification on location of service disconnect? [ 1 Answers ]

My power comes on to my property on a pole that is approximately 25' from my house, down to the meter base and then underground to my house, that conduit comes through the ground in middle of the house( I only have a crawl space) it goes straight through the floor and into the panel, about 5' total...

400 amp service disconnect [ 1 Answers ]

I am installing a 400 amp service (non-residential). Outside of the building I want to put a Combination Service Entrance Device (meter main) with two 200 amp breakers. These breakers will feed two 42 circuit load centers located inside and directly behind the CSED. Do I need main breakers in each...

200 amp service disconnect [ 1 Answers ]

What type of 200 amp service disconnect ( type 3 ) is better, a fused type or breaker type? Are they both available with a knife switch type handle?

200 Amp Outside Service Disconnect [ 5 Answers ]

I NEED TO KNOW IF A "200 AMP OUTSIDE SERVICE DISCONNECT" IS THE SAME THING AS A "200 AMP OUTSIDE MAIN BREAKER OR LOAD CENTER"? SOMEONE PLEASE HELP ME!! HOME DEPOT WAS USELESS.:confused:


View more questions Search