    Installing track lighting
    I want to replace a fluorescent ceiling fixture with a line voltage flexible track kit. There is a WARNNG on the box that says.. Risk of Fire, most dwellings built before 1985 have supply wire rated 60 Degrees Centigrade. Consult an electrician before installing. My dwelling was built in the late 40's or early 50's. Is there any dangers here that I should be worried about?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Aug 12, 2008, 07:19 AM
    What they are telling you is that there is a risk of fire caused by heat.

    There are three temperature grades of wire insulation. 60, 70 and 90 (all Celsius). Residential wire and cables were originally spec-ed out at 60. As the temperature climbs above the rated temp. The insulation can melt or burn. This in turn set up a bare wire arching condition between two conductors and Whoosh, there stands a burnt out shell where a home once was.

    Currently, the NM Shielded cable used has wires that are rated at 90 c. (194 F).
    Tev's Avatar
    Tev Posts: 232, Reputation: 20
    Full Member
     
    #3

    Aug 12, 2008, 01:04 PM
    It should also be noted that the heat being talked about has a combination of sources, the heat put off by the wire itself as current flows through it and the lighting fixtures being two of them.

    My point being, nobody should assume something like this will be OK because "it doesn't get hot in my area". Believe me I've heard it before.
    benaround's Avatar
    benaround Posts: 69, Reputation: 6
    Junior Member
     
    #4

    Aug 12, 2008, 10:41 PM
    Quote Originally Posted by donf
    What they are telling you is that there is a risk of fire caused by heat.

    There are three temperature grades of wire insulation. 60, 70 and 90 (all Celsius). Residential wire and cables were originally spec-ed out at 60. As the temperature climbs above the rated temp. The insulation can melt or burn. This in turn set up a bare wire arching condition between two conductors and Whoosh, there stands a burnt out shell where a home once was.

    Currently, the NM Shielded cable used has wires that are rated at 90 c. (194 F).
    Donf, Thought I would let you know, per 334.80 2005 NEC , types NM,NMC, and NMS shall

    Use the 60deg. Column for ampacity.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #5

    Aug 13, 2008, 09:22 AM
    Yes, but the wires are rated at THHN, 90 Celsius.
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #6

    Aug 13, 2008, 09:36 AM
    Currently, the NM Shielded cable used has wires that are rated at 90 c. (194 F).
    I believe donf was trying to say the conductors inside the Sheathing is rated @ 90 degrees.
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #7

    Aug 13, 2008, 09:39 AM
    Just to add (as mentioned by benaround):The ampacity of Types NM, NMC, and NMS cable shall be determined in accordance with 310.15. The ampacity shall be in accordance with the 60°C (140°F) conductor temperature rating. The 90°C (194°F) rating shall be permitted to be used for ampacity derating purposes, provided the final derated ampacity does not exceed that for a 60°C (140°F) rated conductor. The ampacity of Types NM, NMC, and NMS cable installed in cable tray shall be determined in accordance with 392.11.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Track Lighting: 6 pendant lights/4 sections of track 2 lights not working? [ 4 Answers ]

Hi, Here is the situation. Two light bulbs blew. Our handy man told us that when you replace the bulbs 12v that you can not touch them or they will keep blowing. So we used gloves and changed the two blown bulbs. Voilą! Light. About 3 days later the first one blew again and then the...

Track Lighting [ 1 Answers ]

Do you know if there is a Track Lighting system that allows you to turn individual lights on or off on the track. I would like to have certain lights on the track on in the evening and the rest on the track off.

Installing track lighting [ 3 Answers ]

I just purchased three tracks and a "T" connector. None of the tracks came with a power feed. Is is possible to use the wiring in the "T" connector as the power feed from the junction box? If so, how? Thanks.

Cutting Track Lighting track [ 1 Answers ]

Anyone know why Hampton Bay track states that you cannot cut the track? Every other brand allows track to be cut to the needed length and Hampton Bay is worthless to me if I can't cut it.

Old Track Lighting [ 2 Answers ]

I apparently have an old Murray Feiss track lighting system (3 lights w/reflector bulbs). I was hoping to find a compatible track head, but have been told that there are none. The heads in place now are big and bulky and ugly and would like to replace them. Would it just be easier to replace the...


View more questions Search