    Adding more water pressure to PVC pipe
    I have a home with well water and I have less than ideal water pressure. Are there any special precautions concerning increasing pressure from the current 30/50 to 50/70 in a home with PVC type pipes? I am worried this might overstress the joints.

    Thanks
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Jul 25, 2008, 06:03 AM
    I don't think I'd go any more than 40/60. Tell us more about where you lack pressure, how your system is acting.
    Milo Dolezal's Avatar
    Milo Dolezal Posts: 7,192, Reputation: 523
    Plumbing Expert
     
    #3

    Jul 25, 2008, 06:33 AM
    As far as your PVC pipe goes, it should be OK with 50/70 psi pressure. Depending on what type of pipe you have, common PVC pipe can hold up to 480 psi. However, keep in mind that best residential operating pressure is believed to be 55 psi.
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #4

    Jul 25, 2008, 06:57 AM
    The average house pressure's 45 PSI. This is why most water towers are 100 feet tall. 00 feet gives you 45 PSI at the base amd booster pumps maintain the pressure. On long runs the utility company will increase the main prressure to reach out laying areas. This will force some home owners to install PRV valves to adjust the pressure down to a useable PSI.
    afaroo's Avatar
    afaroo Posts: 4,006, Reputation: 251
    Ultra Member
     
    #5

    Jul 25, 2008, 01:43 PM
    I would like to add the link below,Thanks.

    John

    Google Answers: Residential Water Pressure
    Milo Dolezal's Avatar
    Milo Dolezal Posts: 7,192, Reputation: 523
    Plumbing Expert
     
    #6

    Jul 25, 2008, 06:58 PM
    Quote Originally Posted by afaroo
    I would like to add the link below,Thanks.

    John

    Google Answers: Residential Water Pressure
    Yes, that's a good link. In my area, we are on the high side with our water pressure. It is mandated by our Plumbing Code that pressure regulator is installed when pressure exceeds 75 psi. I cannot recall last time I've seen a house w/o water pressure regulator.
    jlisenbe's Avatar
    jlisenbe Posts: 5,020, Reputation: 157
    Uber Member
     
    #7

    Jul 26, 2008, 05:07 AM
    Danger, I would not want to run a well at over 60. The reason is the stress you are putting on your pump. Besides, 60# is plenty of pressure.

    It is simply a given that living on well water is not going to be the same experience as living on municipal water.
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #8

    Jul 26, 2008, 05:26 AM
    I have read where 100 PSI is a acceptable house pressure. I strongly disagree.
    Milo says,
    It is mandated by our Plumbing Code that pressure regulator is installed when pressure exceeds 75 psi.
    There's a reason for that, it puts too much of a strain on the fittings, joints and valves when the house pressure runs too high.
    The average house pressure's 45 PSI. This is why most water towers are 100 feet tall. 00 feet gives you 45 PSI at the base amd booster pumps maintain the pressure
    I agree with jlisenbe that 60 PSI should be enough pressure to service any home. I urge every homeowner with a PRV valve to purchase a hose bib pressure gage,(see image) and check the house pressure on a regular schedule. Good luck, Tom
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #9

    Jul 26, 2008, 06:19 AM
    Well, I'm waiting for Danger to come back and tell us what his problem really is, so we can tell him to clean his aerators.
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #10

    Jul 26, 2008, 06:54 AM
    Quote Originally Posted by hkstroud
    Well, I'm waiting for Danger to come back and tell us what his problem really is, so we can tell him to clean his aerators.
    This could also be a low volume problem caused by old galvanized piping. We answered his question about the extra pressure. Now it's up to him to let us know if he has more questions. Regards, Tom

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Water pressure burst pipe? [ 2 Answers ]

Is it possible if when you shut service off at the meter and then turn it back on too quickly,it can cause your line to burst?

Pipe diameter = poor water pressure? [ 1 Answers ]

My apartment has low pressure, especially in the shower. It's a loft building in NYC and my unit was renovated in 1985. Others in the building claim to have no issues with pressure. I'm re-doing one bath and the walls have been removed. While the pipes running to the shower area are large, the...

No water pressure after pipe replaced [ 1 Answers ]

Hi--we had a leak in a hot water pipe in our basement--after the pipe was replaced we have lost our hot water pressure. The pipe is more narrow than the pipe that was originally there, could that be the problem?


View more questions Search