    #1

    Jul 21, 2008, 01:14 AM
    Drop in drain pipe
    I am wondering what the general rule is on how much a kitchen sink drain pipe should drop every 10 ft? I am relocating my kitchen and when I looked at the new 30 ft. kitchen sink/ garage disposal drain pipe under the house the total drop was only 1/2". It appears to almost sit level across the pipe span. I am afraid my kitchen sink will not drain properly and will back up if this pipe doesn't have more of a drop over the 30'.
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #2

    Jul 21, 2008, 04:03 AM
    Hi mamadog:

    All plumbing pipes 3 inch and smaller are required by ALL plumbing codes to have 1/4" pitch per foot of piping.

    In the case of a 30 foot run of pipe from kitchen sink you would therefore require a minimum of 7.5" pitch to the pipe. This pipe should also have hangers every 4 feet.

    Sounds like the new work hasn't been inspected... ;) Also wondering what size pipe (best size is 2" pipe, but 1.5" is allowed in some areas) was run and if you will have a garbage disposal? Lastly, you should also have a full size cleanout UNDER the kitchen sink and another cleanout in the basement at any major change in direction in the piping.

    Who piped this drain.. How is the sink vented?

    Let me know what you can...

    MARK
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #3

    Jul 21, 2008, 04:52 AM
    Quote Originally Posted by mamadog
    I am wondering what the general rule is on how much a kitchen sink drain pipe should drop every 10 ft? I am relocating my kitchen and when I looked at the new 30 ft. kitchen sink/ garage disposal drain pipe under the house the total drop was only 1/2". It appears to almost sit level across the pipe span. I am afraid my kitchen sink will not drain properly and will back up if this pipe doesn't have more of a drop over the 30'.
    Your pipe should slope 2 1/2"every ten feet for effective drainage. This works out to 7 1/2" for a 30' run at 1/4" to the foot fall. The configuration that you have almost guarantees you problems especially if you have a disposal installed. As Mark pointed out while 1 1/2" is acceptable in some areas a 2" kitchen drain is what we normally put in. For some time now our local code has mandated a 3" drain for kitchen drainage. This came about with the advent of garbage disposals. This 3" drain was extended up to become the main house vent as reguired by our code. While we don't require cleanouts it's a very good practice to install them. Would it be possible to call your installer back and have the job done correctly? Good luck, Tom

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

My Well Pump Keeps Busting the Drop Pipe? [ 24 Answers ]

HI, I put a new pump in my well in Dec.2007, so far it has busted the drop pipe THREE TIMES :mad: Can't figure it out. I know its something to do with pressure, but what, when I cut the old busted piece off, and reinstall the pump it usually lasts 4-5 days and does it again, I have close to 300 ft,...

Main drain degree of drop [ 1 Answers ]

I'm finishing my basement and the main drain pipe is in a very bad spot. I'm going to re-run the main drain. How much of a drop should the pipe be? (Example: 1" every 10')

Vent pipe turned into drain pipe and drain pipe into vent pipe [ 3 Answers ]

I recently began to remodel my laundry room. I wanted to move the washing machine 3 ft from its current spot. When I removed the sheet rock I found that the vent pipe is between the current washing machine drain and where I am moving my washing machine. I wanted to avoid breaking into the slab....

Shower pipe broke off in drop eared ell [ 4 Answers ]

Any suggestions on how the get the threads out of the ell? I was investigating a leaky shower head and it ended up being the pipe and ell. The pipe had a break near the ell and while trying to remove it, it broke off. Thanks

Shower drain drop to drain [ 2 Answers ]

We are replacing our bathtub with a shower. The shower drain hole is in the center, whereas the bathtub drain was at one end, we intend to use the same drain in the cement foundation, but we need to know how much of a drop that is needed from the new shower drain to the original drain. We are...


View more questions Search