    Brand NEW condenser/coil - still warm air
    I just had a brand new 2008 goodman unit - complete condenser and coil. Yes it is on the roof but that's my only option. I have 1200 sf and vaulted ceilings. I believe we removed the 1 ton and put in a 2 ton. It cools off enough at night that AC isn't really needed until about 10AM then by noon a setting of 78 reads 80 and by 2pm it reads higher and the air isn't even cool anymore... by 5:30 its 85 on the reading though the front room is warmer than that. Finally when the sun has set it starts cooling off. The force of the air never really changes - its just that from 12-5:30 the air is warm and more or less not worth having on. I mean my fans are still on and it feels the same as if I hadn't made the investment. HELP? Is the 2 ton too small? Is it really the furnace fan? I've been told everything that it will always be 20 degrees cooler inside. But how can the air temp change so dramatically for 5 or so hours while the force is the same? Need advice...
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jul 19, 2008, 07:54 PM
    Did you talk to the professional contractor that installed your equipment?

    Did he take into consideration the fact that you have vaulted ceilings?

    You have a design problem that should have been corrected.


    A 1200 square foot home of normal construction will take 2 to 2 and a half tons. You have a different animal.

    The air discharge stays the same but the temp will change because the return air temperature is going higher due to the heat load increasing.

    I would contact a engineer or another HVAC company to do a ON SITE inspection since all we can do here is guess what your problems really are.
    jscarpe's Avatar
    jscarpe Posts: 5, Reputation: 1
    New Member
     
    #3

    Jul 19, 2008, 09:23 PM
    Thanks hvac1000
    That's what I thought but he's told me various "technical" explanations - shouldn't it be cubic area vs. square footage when dealing with this footprint? I've spoke to them - yes, they came out once since the install, one week passed before coming out again - but today was almost 100 degrees and so I'm searching for more answers - hopefully the right ones. 1200 sq ft actually 600 at 25 feet and then 300 and 300 with regular close to std heights. Well they are coming again - then the city still has to come and inspect - perhaps their point of view will be useful. Oh... he said a 2.5 would freeze??
    jscarpe's Avatar
    jscarpe Posts: 5, Reputation: 1
    New Member
     
    #4

    Jul 19, 2008, 09:37 PM
    Oh... 300 is the open loft adjacent the 600 at 25ft. The other 300 is at std ceiling heights.
    Yes the vents upstairs are a little weaker but not much - a little cooler but not much than below... right now its cooler outside after running AC all day! What a waste finanically and environmentally.

    I'll be curious what they say tomorrow mid day - I'll take notes for sure.

    I've heard it all
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Jul 20, 2008, 03:23 AM
    I mentioned this

    Did he take into consideration the fact that you have vaulted ceilings?

    I also mentioned this

    A 1200 square foot home of normal construction will take 2 to 2 and a half tons. You have a different animal

    Actually the salesman/installer should have done a manual J for the equipment size to start with.

    Then they should have done a manual D for the correct duct work size and placement.

    I have said this way to many times. Always get 2 or 3 estimates because you might actually find one of them that knows what they are doing.

    Remember cold air falls like a rock no matter how much you try to blow up there it will never stay there. You are a prime candidate for a large high return air system to scrub that heat off the highest point. This will cause the system to draw the heat out of the upper level and replace it with cooler air.

    Then you will be a happy camper. But remember that the equipment will still need to be sized by a manual J.

    For your viewing pleasure.

    HVAC Sizing Practice


    EERE Consumer's Guide: Sizing Heating and Cooling Systems
    jscarpe's Avatar
    jscarpe Posts: 5, Reputation: 1
    New Member
     
    #6

    Jul 20, 2008, 06:29 AM
    I got 3 estimates - with huge ranges in price but with all the same recommendations - no one did a manual j or anything like that. From big name brand to a one man show type of company. This person actually recommended the most improvements w the best price too. Sounded knowledgeable. Thanks again for your input.

    What makes a unit that is too big freeze - that is what he said last but wasn't for sure either.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Does a 3 ton coil match up with a 2 ton condenser unit [ 19 Answers ]

I have a new Payne brand 2 ton central air unit that was installed by my home warranty company, and after two months and after they sent out three different companies to try and fix my cooling problem, the last company decided that the original Carrier brand system that has been in my home for 26...

Honda XL-250 (1976) Coil (drilled out rivet to mount condenser) [ 1 Answers ]

I looking to buy a neighbors 1976 xl-250. A local shop suggested he buy a new condenser which he did and wired it to the coil. The bike started and ran fine but the new condenser was hanging from it's one lead. The owner thought he'd clean it up and drilled out the rivet that held the mount for the...

Does a 4 ton evaporator coil match up with a 3 ton condenser? [ 1 Answers ]

We just moved into an 11 year old house last month. The AC has not worked properly since we moved in. The first AC guy the Homeowners Warranty company sent cleaned the unit and added freon. A month later, it was 83 degrees downstairs today. Last week they sent another guy and he found what he...

New Outside Condsing Unit, Bad indoor Coil - Go with Heat Pump or Buy New Coil? [ 7 Answers ]

Hi All, Here is my issue. Recently, our home warranty company paid to replace a 25 year old 7 SEER Borg Warner outside unit, but swore up and down that the indoor Borg Warner Coil would be OK with the new 10 SEER Carrier. We no longer have this home warranty company and they are not standing...

Copper Condenser Coil [ 1 Answers ]

Is it possible to solder a hole shut in the copper tubing that feeds freon throughout the coil? I believe the hole in the pipe that runs verticle from the compressor to the coil. Thanks. Dave


View more questions Search