    Mar 25, 2006, 11:17 PM
    Testing circuits
    Anybody have creative ideas on how to test light and receptacle circuits in a brand new house that does not have power yet from the utility company.

    The sub panel is complete with all the wires and circuit breakers connected. All the receptacles and lights switches are installed.

    Has anyone ever used a extension cord and removed the female end and connected the neutral wire to the neutral bar I sup panel and ground wire to ground bar and pigtail the hot to connect to a installed breaker on each phase? Turing on the breaker would send power to all the other breakers.

    Thanks.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Mar 26, 2006, 05:21 AM
    What you propose is possible, however, can cause problems if you are not careful. If the power to the home has not been connected, where is the power coming from,a generator?

    You must be sure to shut off the main breaker, or you will send power out to the meter socket, or to the incoming wires, that may have exposed parts.

    If you are sure of the entire system has no exposed parts, then, for testing purposes your method would work.

    Be sure the system has been inspected and belongs to you. If I were the electrician that installed the system, and it has not been inspected and released to the owner, I have the permit and "own" the system until such time it has been energized,tested,inspected and released, and would not warranty the system should I discover a non-licensed person has opened the panel and modified my connections.
    loupi01's Avatar
    loupi01 Posts: 92, Reputation: 1
    Junior Member
     
    #3

    Mar 26, 2006, 10:21 AM
    Thanks tkrussell,

    For testing the power will come from a extension pole that will be plugged into temporaty power setup by the utility company. Temp power comes into a circuit breaker and out to 2 GFI receptacles. The only thing left to do on this new house is to have the utility company come out run their wire to the meter on the outside of the house. I wanted to test (with electircity) the all the circuits in the subpanel. My first option is to go to a receptacle that I know is fed from the suppanel and energize it with an extension cord. And then test all the receptacles and lights on that circuit.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Mar 26, 2006, 12:25 PM
    I would prefer you did an extension cord plugged into an outlet than be opening panels that have been assembled properly, taking a chance to create problems down the road.

    I can understand trying to test the circuits, could be for several reasons. If done safely and eyes wide open, and being monitored until completed, using a cord with two males will work fine.

    Best to use as the input the any GFI outlet, and of course at the source. Not sure how the two GFI will react, but it will be safe, and if both work, can be a very good test of the entire system.

    As I think of it,the GFI's may not work because of the length of the wiring, high impedance will cause the GFI to trip.

    Be sure to shut off the main, and lock it off until the test is complete.Do not energize any 240 volt loads. Do not turn on more than what you are testing.

    You will need to find two outlets that are on opposite phases.

    Be safe.
    loupi01's Avatar
    loupi01 Posts: 92, Reputation: 1
    Junior Member
     
    #5

    Mar 26, 2006, 11:17 PM
    Thanks tkrussell again for all your help

    I would like to tell all who is reading this post that what we talked about here is extremely dangerous and would not recommend anyone to attempt this unless they are confident in there ability and knowledge of electricity.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Circuits [ 2 Answers ]

Suppose that the switch has been closed for a length of time sufficiently long for the capacitor to become fully charged. (a) Find the steady-state current in each resistor. R1=16.00 kΩ, R2=12.00 kΩ, and R3=2.00 kΩ. (b) find the charge on the capacitor. 9.00V, 10.0uC I found part (a) but I'm...

New bathroom circuits [ 1 Answers ]

I am remodeling my 2nd floor bathroom and adding laundry (gas dryer). I replacing old circuits with 2 new circuits. One dedicated to washer/dryer and another for one outlet, 2 vanity lights, 1 general illumination light, and for the exhaust fan/shower light. Can I make one 12/3 run from my...

'Cross line' in circuits [ 2 Answers ]

I would like to know if it's possible for 'cross line' or contamination (don't know if it's the correct word) to exists in electrical systems just like in a telecommunication systems when one person phones the other person and one or both of these parties can sometimes hear the conversations of a...

Number of circuits [ 5 Answers ]

I’m in the process of remolding my basement, basically 2 20x20 rooms. My question is how many separate circuits do I need for the electrical. All I’m talking about is lights and general use outlets. Could all the lights and outlets be on one circuit, or should they be separated? By room or by...

Circuits in Kitchen [ 6 Answers ]

I just replaced my appliances in my kitchen and when installing the Fridge they had to plug it in to a different outlet from before. I didn't think it should share an outlet - but I looked at my circuit box and there doesn't seem to be a dedicated Fridge outlet. The electric range is on it's own...


View more questions Search