    Exterior Plumbing Vent Stacks
    How far should they be above an operating door?
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #2

    Jun 25, 2008, 09:47 AM
    Are you talking about the termination of the vent of just where it runs. Stacks should terminate above the roof line.
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #3

    Jun 25, 2008, 05:26 PM
    Here's how my code book calls it guys (Massachusetts, Uniform State Plumbing Code, 93):

    "No vent terminal shall be located directly BENEATH any door, window, or other ventilating opening of the building or of an adjacent building NOR shall any such vent terminal be within TEN FEET horizontally of such an opening unless it is at least TWO FEET above the top of such opening"...

    So basically, if your vent terminates TWO feet above doorway and no other windows/ventilating openings above the door... you are all set by code.

    Any window/air intake above that door must be farther away than TEN FEET horizontally for you to terminate your vent above the door.

    Code in your area may differ slightly... but I bet not by much... so, If you can't meet these requirements... then as Ballenger said... must terminate vent through the roof.

    All vent penetrations must be 2" minimum size pipe... and if going through roof... should extend to between 18" and 24" maximum through roof.

    Hope that answered the question..

    If not, was fun to post this info. Anyway... ;)

    If not, let us know what you can... :)

    Mark
    westnlas's Avatar
    westnlas Posts: 322, Reputation: 25
    Full Member
     
    #4

    Jun 25, 2008, 05:36 PM
    24 inches above the roof at the point it emerges sounds as I remember also. Chimney stacks are determined by a point of roof a distance away. "Mass" nailed this one for you. I remembered that the stack cannot be within 6 feet of an attic vent or must be above it 2 feet also. I think it may be true for air conditioning units and swamp coolers too.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Exterior plumbing stack vents [ 8 Answers ]

How far from above operable doors and windows should exterior plumbing stack vents be?

Exterior Plumbing Vent, should there be a visible pipe? [ 9 Answers ]

We recently had a half bath installed on the first floor of our home. For a variety of reasons, we asked that the vent be put through the exterior wall as opposed to going up through 3 floors and through a slate roof. My question: our contractor says that the vent is there, but all I see is a...

Exterior plumbing vents [ 2 Answers ]

Should exterior plumbing vents be at least 3 ft above operable doors and windows?

Plumbing Vent [ 1 Answers ]

Does anyone know how I can get my plumbing tube vent through a 2x4? Thanks in advance.

How do I cut through exterior wall to add second bathroom sink plumbing? [ 1 Answers ]

I am remodeling my master bathroom and want to add sink. Currently, there is one set of pipes for a sink and would like to splice them into a second sink. The problem is that the current plumbing is located in an exterior wall and I need to know how to cut open the wall, so that I can expose the...


View more questions Search