    Pulling #4 Wire in 11/4" EMT
    When I started this project I was looking at running #6 TTHN in 1" conduit. But many of you feel #4 would be more acceptable for a 60amp sub-panel at 120-150 feet away.
    So......
    Now, I am looking at 11/4" Conduit and 4-#4 wires(2 hots #4, 1 Nuetral #4, and #4 Ground) I could probably size the ground down, but in the scheme of the overall project the cost is minimal.
    I have pull wire through smaller Emt(eg. 1" #8) but have never pulled #4 thru 11/4" EMT for this long of a pull.
    My question is--I would suspect I would need j-boxes in the raceway because to pull that size wire 150' feet is going to get interesting. My bends from the service panel to house center will entail 270 degrees of bending. Then I have 120 feet of straight with no bends and to finish with a 90 degree at the end into a QO Sub-panel box.

    Would I use J-Box every 50'? Or what would be your suggestions to make my pulling easier?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Jun 5, 2008, 02:45 PM
    Quote Originally Posted by cc4digital
    Would I use J-Box every 50'? Or what would be your suggestions to make my pulling easier?
    I would NOT install boxes every 50'. NO way.

    Use wire lube and have a good helper.
    A #4 ground is WAY overkill! NO reason AT ALL to have that. Use a #8 with the #4 feeder.


    What is your load at 120'? I think #4 is overkill.
    If you use #6 then a #10 ground is all you need.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Jun 5, 2008, 05:06 PM
    You don't use J-boxes, however you can use conduit bodies such as these hdsupplysolutions.com

    Or variations for elbows.

    Use plenty of lube.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Pulling wire through conduit [ 9 Answers ]

I have to pull 3, #4's and 1, #8 (150' ea.) through 1 1/2" PVC. There are 2, 90 degree bends. Am I better off to pull 1 or 2 wires at a time, with a additional pull rope, or just pull all 4 at one time. I have plenty of lubricant available. Comments? Suggestions? Thanks

Replacing old "General Controls" thermostat. How to determine what the wire do? [ 5 Answers ]

I am replacing an old "General Controls" thermostat, model T-90H110A137, 24 volts max, 0.8 AMP. The wires are labelled but not to the current standard of H1/H2/B/O/RC/RH/G/Y/W. how do I determine which wire is for what? The old thermostat controls a furnace and has a continuous fan option. ...

Pulling wire in pvc [ 1 Answers ]

How many # 6 thhn can you pull in 3/4 pvc

Pulling wire through conduit [ 2 Answers ]

I currently have 100' of 10/2 UF cable running underground through 3/4" PVC conduit. I need to pull the 10/2 out, and pull in 10/3 UF (or its code equivalent) to replace it. I have 3 questions: 1) Is 10/3 UF cable always produced in a flat configuration, or does some company manufacture a round...

Thermostat -- What is the "X" wire? [ 1 Answers ]

On my old Rheem thermostat there's 7 wires: Green - G Red - R Blue - B Yellow - Y Brown - X White - w2 White(looks like its just jumped from e to w2).


View more questions Search