    Am I overcharging AC or defective TXV?
    Fired up my 5 ton Carrier AC. Low side showed 50 PSI for a couple of hours then drops to 15-20 PSI. Assume freeze-up.

    Defrost

    Today I start adding R-22 (slowly). For the longest it never went above 55 PSI. After about an hour at 55 PSI it would jump to 75 PSI & slowly descend back to 50 PSI. Stopped adding R-22.

    Shut unit off for about an hour. Restarted and low side shows 75 PSI. Slowly drops to about 65 PSI. VERY Confusing. Connect gauges to high side. Gage jumps to 300 Psi and SLOWLY climbs to 400 PSI. However low side barely changes. Indoor air around 75 Degrees.

    That is where I am now. THANKS for any replies.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    May 27, 2008, 12:26 PM
    Sounds like non condensibles in system. Contact someone with a EPA certificate to perform work with R-22.
    billyboyfeb's Avatar
    billyboyfeb Posts: 4, Reputation: 1
    New Member
     
    #3

    May 27, 2008, 12:36 PM
    Quote Originally Posted by hvac1000
    Sounds like non condensibles in system. Contact someone with a EPA certificate to perform work with R-22.
    How can that be? The system has been working fine for about 3 years with no problem. Where would it get non condensibles?
    Thanks
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    May 27, 2008, 12:54 PM
    Any thing can happen. Contact a professional to have your system serviced. It could be a valve but TXV's do not go bad very often. There are many other possibilities.
    Dirty indoor coil.
    Dirty filter.
    Floater in system (Dirt). It can break loose any time.
    billyboyfeb's Avatar
    billyboyfeb Posts: 4, Reputation: 1
    New Member
     
    #5

    May 27, 2008, 12:55 PM
    Quote Originally Posted by hvac1000
    Sounds like non condensibles in system. Contact someone with a EPA certificate to perform work with R-22.
    Also could it be an overcharge combined with a bad TXV? It does have an inline filter in the High side which should trap floaters. I guess that it could also be clogged.
    Thanks.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    May 27, 2008, 12:57 PM
    Anything is possible.
    billyboyfeb's Avatar
    billyboyfeb Posts: 4, Reputation: 1
    New Member
     
    #7

    May 27, 2008, 01:11 PM
    Quote Originally Posted by hvac1000
    anything is possible.
    Runtime Pressure Chart
    Min:Seconds Low Side High Side
    0:30 85 300
    1:00 74 290
    1:30 72 280
    2:00 70 285
    2:30 70 310
    3:00 69 340
    3:30 68 325
    4:00 68 330
    4:30 68 360
    5:00 68 370
    5:30 68 375
    6:00 68 385

    Got scared. Shut down unit
    Sorry to be such a pain in the A, but there is only 1 AC serviceman within 30 miles (Rural Texas) & I know that he will take advantage of his mother or anyone else. If I have enough knowledge, maybe I can keep him halfway honest.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #8

    May 27, 2008, 02:24 PM
    Sounds like the area need more qualified service persons. Good luck.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

My landlord is overcharging on my Utilities. [ 7 Answers ]

I live in a small poolhouse that my landlord's family turned into a studio. Approximate size is 25 feet by 25 feet. I have been living there since early 2001. To this day, my landlord has never given me a copy of her electric/gas bill and she has never given me a copy of the water bill. She...

Can property damage charges be dismissed if landlord tries overcharging you? [ 2 Answers ]

I received a bill from an apartment complex I used to live in for $910.74 for carpet damages caused by a pet. the original bill they sent me stated they were charging $1060.74 against my $150 deposit due to Carpet charges: ($1586.67/60 ms (life of carpet) = 26.44x37 ms of life= $978.28) plus...

AOL Overcharging me? [ 4 Answers ]

Hi everyone, I need some advice, or even just opinions. I have been an AOL customer for years now, and I upgraded to AOL gold almost 2 years ago. When I signed up I was paying £19.99 a month instead of the standard £24.99 a month the package cost back then. However AOL have rduced the package...

95 dodge dakota 4cyl is overcharging! [ 4 Answers ]

Hello! I have a 1995 dodge dakota sport, 4cyl 5 speed with a problem that no mechanic will touch! I have replaced the alternator, computer ECM(has the voltage regulator built in), wiring to the altenator, a new fuel pump, distrubtor, pick-up coil, new battery and connectors to the battery. My...

1995 Jeep Wrangler 4.0L - overcharging [ 2 Answers ]

For several months my charging gauge read at or near the red-line. Over the past week it is almost pegged-out if no lights or heat is on (when lights and heat is on it drops to 16-17, but still in the red). I replaced the battery and altenator but the problem still persists. All other guages appear...


View more questions Search