    Changing 15Amp outlet to 20Amp
    Recently had a generator installed for the business. Electrician mistakenly added 15amp power outlet within the generator housing unit. Need to change this to 20amp to plug in the block heater. My assumption is that the breaker is a 15amp breaker. If we change the outlet at the generator, will we have to make sure the breaker is 20amp also?. or can we get away without doing this?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    May 23, 2008, 07:42 AM
    You actually do not have to change the outlet if you don't want to. A 15 Amp receptacle can handle 20 Amps.

    However, the same is not true of the Breaker and the conductors to the receptacle. 15 Amp cables use #14 AWG conductors. To use 20 Amp, the conductors have to be changed to #12 AWG and the breaker to 20 Amps.

    A #14 AWG cable becomes a fire hazard if you run 20 Amps through it.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    May 23, 2008, 07:43 AM
    For a 20 A load the wire size has to be 12 AWG and the breaker must be 20 A.

    You can, however, have a 15 A outlet, 12 AWG wire and a 20 Amp breaker.

    The breaker protects the wiring: 12 AWG wire, 20 A breaker allowed; 15 A breaker allowed; Receptacle rating should not be less than breaker rating.

    14 AWG wire, 15 A breaker, 15 A receptacle.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #4

    May 23, 2008, 07:49 AM
    Donf:

    I challenge you to find me a spec. where a NEMA 15-5R receptical is rated for 20 amps.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Changing 15amp outlet to 30 - will it work? [ 4 Answers ]

Our gas dryer just went out and we have an electric one in the shed. When we brought it in to plug it up the plug was not the same kind as the outlet. (The gas dryer was plugged into a standard outlet with the washer.) The electric dryer's cord has an L shaped prong but the outlet has what looks...

15AMP Breaker used instead of 20AMP -ok? [ 4 Answers ]

We just had an electric gate installed that extends across our driveway. I noticed that the installer used a 15 amp breaker switch to connect to for power (the gate is the only device on this breaker). In looking at the manual last night the installation instructions call for a 20 AMP breaker (the...

20amp vs. 15amp outlets [ 6 Answers ]

Is there anything inherently different between 15amp and 20amp outlets? Outlets labeled 20a are about 3-4 times more expensive than the ones labeled 15a. My buddy with a fair amount of experience advises me to buy 15a outlets and hook them up to my 12 gauge wire running back to 20amp breakers. ...

15amp or 20amp? [ 2 Answers ]

Does the 2005 NEC allow bedroom and living room outlets to be on a 15amp circuit? I am familiar with the 80% rule. Thanks in advance. Tom

Outside GFI circuit - 15amp outlet on 20amp circuit [ 1 Answers ]

I need a better understanding of what I should do when setting up my new outdoor circuit. I've got a circuit that runs about 150 feet, so I'm installing 10g wire to allow for the voltage drop. I read in the Home Depot Electrical 123 book that I can have at most a 15amp circuit with 10g wire on...


View more questions Search