    Bare ground in box
    Quick question... When one is running the ground out of a sub panel to the ground rod, does it matter if the bare ground wire is touching the panel box?

    Some have told me that it does matter if the bare copper ground is touching the panel box . But I ask them how hell your suppose to run the gnd wire and have it NOT touch the punch outs? I installed it by just knocking out a small knock out plate and running it out the bottom that way. Makes no sense to me that this will hurt anything.

    Are they right? OR is this just a wasted post because I know better!
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    May 7, 2008, 05:36 PM
    Who ever would say that has NO clue.

    You are correct.
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #3

    May 7, 2008, 06:56 PM
    I agree.

    No clue!

    You must have spoke with someone from HD! :)
    mr500's Avatar
    mr500 Posts: 181, Reputation: 8
    Junior Member
     
    #4

    May 7, 2008, 08:39 PM
    Quote Originally Posted by Washington1
    I agree.

    No clue!!

    You must have spoke with someone from HD!!:)
    Pretty much. It was the same guy that told me I could put my Neutral and Gnd on the same buss in the sub panel. SOOO I should have known. Tried to tell him that the equipment gnd was bonded to the panel, so why would it hurt for the wire to touch. Made no sense to ME!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bathtub construction: no slab, bare ground [ 3 Answers ]

After Mold Remediation and new construction: still have the mold smell. During remodeling, after mold remediation (done by a national, reputable company) on my daughter's bathroom/vanity area, where there was a leak under the vanity and a lot of mold growing in the vanity and behind the vanity...

Using the ground or (bare) wire for the neutral wire [ 2 Answers ]

I have a problem with some wiring that I ran for an outside motion light. Although the hot leg and ground wires are fine, the neutral wire is defective ( it may have gotten knicked or something). Of course, now the wiring is covered up behind a wall that I do not want to tear into if it can be...

Is it okay to use bare wire as neutral? Okay to share ground? [ 53 Answers ]

Our house was built in 2003 and it came with a GE 24" microwave oven that uses 120 volts/20 Amp. The microwave stops working so we went out and bought a KitchenAid convection microwave oven that requires 20 Amp, 240 volts, 60 Hertz. The old microwave oven uses 12/2 w/g romex from a subpanel. ...

Have anyone used bare minerals [ 9 Answers ]

Have any 1 use bare minerals or know someone who did?. Can you please let me know... if you did or some else and ti really help to impove your skin. It's a make_up.


View more questions Search