Ask Experts Questions for FREE Help !
Ask
    LeftyMoe's Avatar
    LeftyMoe Posts: 3, Reputation: 1
    New Member
     
    #1

    Apr 1, 2008, 02:40 PM
    Rheem Criterion thermal switch keeps tripping
    Recurring intermittent problem: Furnace runs properly, but more and more often, the thermal (350 deg) switch above the leftmost burner trips, which causes the blower to stay on and the furnace to NOT re-light when the thermostat calls for another cycle. I can reset the switch (depress the small plunger) and it will work fine for a few cycles, but then trips again. I replaced the switch, but still the same problem. Any thoughts? Thanks.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Apr 1, 2008, 04:53 PM
    If the furnace was operating properly the thermal safety device would not trip.
    Usually that is a indication of to high a temperature in that area.
    When was the last time the gas pressure was tested? ((You did not state what kind of fuel the furnace uses.))

    To high of a firing rate will cause this problem.

    If the flue pipe clear of all obstructions? A back up in the furnace exhaust/flue pipe can also cause this problem.
    It is possible that the burner orifice on the burner tube right below or next to the limit might be partially restricted not allowing the burner to run a full capacity allowing some of the heat to roll out of the burner area and tripping the switch.
    LeftyMoe's Avatar
    LeftyMoe Posts: 3, Reputation: 1
    New Member
     
    #3

    Apr 2, 2008, 01:24 AM
    ((You did not state what kind of fuel the furnace uses.))

    >>Too high of a firing rate will cause this problem.

    If the flue pipe clear of all obstructions? A back up in the furnace exhaust/flue pipe can also cause this problem. It is possible that the burner orifice on the burner tube right below or next to the limit might be partially restricted not allowing the burner to run a full capacity allowing some of the heat to roll out of the burner area and tripping the switch.>>

    It's natural gas. I don't see any obstructions. I think the comment about the heat "rolling out" is viable, but I don't know what to do about it. Any suggestions? Thanks for the response.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Apr 2, 2008, 01:38 AM
    So you can see inside the exhaust pipe that goes outside. I never could do that. I always had to look outside then fish a wire electricians tape from inside to out to be sure of no obstructions.

    Since I am not there I cannot tell what might be causing you roll out situation. It will probably be something that will call for a visit from your local HVAC pros.
    LeftyMoe's Avatar
    LeftyMoe Posts: 3, Reputation: 1
    New Member
     
    #5

    Apr 2, 2008, 08:35 AM
    That may be it... something in the flue causing backpressure/excessive heat? I think I'll call the service guy. Thanks for your replies.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Criterion II Rheem LED signal [ 3 Answers ]

I do not have an operations manual nor can I find one online that will tell me what it means when my Criterion II heater has a LED light that flashes 4 times and will not kick on. I can get the heater to come on by jiggling wires, but once it goes off again, it will not come back on. The heater is...

Rheem Criterion II blower won't stop [ 4 Answers ]

I have a Rheem furnace and the low speed fan continues to stay on after the furnace has cycled off. When I disconnect the red wire (low speed wire), the furnace runs normally. I would imagine the switch for the low speed is open. Is the switch controlled by the IFC? Does the IFC need to be...

Furnace rheem criterion [ 1 Answers ]

Furnace blower fan and the pre blower fan come on at same time. And the ignitor won't light. Have to turn off power switch to stop both fans. I changed upper limit swith but still won't work. When it was working it was going great, returned and blower was running only but no heat. Thermostat...

Do you know the rheem criterion 2 (RDGD 05MAUER) [ 4 Answers ]

Anyone know the rheem criterion 2 (RDGD 05MAUER) , if so could you see my post with pictures on here https://www.askmehelpdesk.com/heating-air-conditioning/heater-fine-daytime-stops-night-159346-new.html I can't figure this out, all the details there if u browse over the posts and reply...

Rheem criterion furnace [ 3 Answers ]

My air went out yesterday and I don't what to do... the motor outside is not working but the inhouse fan is work air is coming out of the vent but it is not cool. This happened in the winter and we had the heat ignaitor replace... help?? it 98 degree today


View more questions Search