    Gas Furnace - gas will not flow after HSI lights
    Goodman Furnace
    Direct Ignition
    - Blower kicks on
    - pressure switch works
    - HSI heats up for about 8 secs -- NO GAS
    - HSI goes out

    Status light just blinks slowly, continuously until I let go of the panel switch.
    Gas valve is ON - ball cock is open - plenty of gas pressure (hot water works right next to it)

    Any way I can check the gas valve for flow?
    Any other suggestions?
    Thanks - Brian D.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Mar 24, 2008, 09:00 AM
    Quote Originally Posted by BCDurbin
    Goodman Furnace
    Direct Ignition
    - Blower kicks on
    - pressure switch works
    - HSI heats up for about 8 secs -- NO GAS
    - HSI goes out

    Status light just blinks slowly, continuously until I let go of the panel switch.
    Gas valve is ON - ball cock is open - plenty of gas pressure (hot water works right next to it)

    Any way I can check the gas valve for flow?
    Any other suggestions?
    Thanks - Brian D.
    How many blinks? Put the panel on and then run test the furnace. Now how many blinks? The schedule of blinks should be listed on the diagram on the back of the blower door but just in case there is a list below. One more thing. Do you have gas present before the gas valve?
    Attached Images
  1. File Type: pdf GOODMAN%20BLINKS.pdf (19.5 KB, 248 views)
  2. BCDurbin's Avatar
    BCDurbin Posts: 27, Reputation: 1
    New Member
     
    #3

    Mar 24, 2008, 01:13 PM
    Just blinks slow and steady - like it is not showing a fault. I have the details showing me what the blinking means but I am not getting a fault. I will try again. I have gas before the valve - it was working just last week - now it doesn't. I just don't get any gas flowing after HSI light-up. Thanks - BCD
    BCDurbin's Avatar
    BCDurbin Posts: 27, Reputation: 1
    New Member
     
    #4

    Mar 24, 2008, 01:15 PM
    Quote Originally Posted by BCDurbin
    just blinks slow and steady - like it is not showing a fault. I have the details showing me what the blinking means but I am not getting a fault. I will try again. I have gas before the valve - it was working just last week - now it doesn't. I just don't get any gas flowing after HSI light-up. Thanks - BCD
    Maybe I'm only getting one (1) blink! Without a fault, should the light be on/off/or blinking at all?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Mar 24, 2008, 02:02 PM
    On all the time (steady light)is the indication that nothing is wrong according to the circuit board. So if you are only getting one blink then is that blink just keep blinking one blink with a pause then another blink all he time. If so then refer to the posted blink schedule.

    If you just loosen the gas line a bit you will be able to tell if you have gas. OR if your gas water appliance or any other gas appliance is working then you should have gas. Is this natural or propane. If propane be very careful.
    BCDurbin's Avatar
    BCDurbin Posts: 27, Reputation: 1
    New Member
     
    #6

    Mar 25, 2008, 08:37 AM
    Quote Originally Posted by hvac1000
    On all the time (steady light)is the indication that nothing is wrong according to the circuit board. So if you are only getting one blink then is that blink just keep blinking one blink with a pause then another blink all he time. If so then refer to the posted blink schedule.

    if you just loosen the gas line a bit you will be able to tell if you have gas. OR if your gas water appliance or any other gas appliance is working then you should have gas. Is this natural or propane. If propane be very careful.
    Natural Gas - water heater on same split line coming into the garage. For some reason the gas valve is not getting the signal to open. Vacuum switch works and HSI comes on but no gas.

    One blink says gas flow/pressure/valve or flame sensor. Flame sensors has been changed and has been checked.

    There are two wires going into the valve - is there any way to check those with a meter to check electricity to them?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #7

    Mar 25, 2008, 10:30 AM
    Look for 24 volt at the valve. Turn off furnace and Hook up your meter directly to the valve wires that you have removed from the valve. Turn on power and Run furnace through a new complete cycle. You should have voltage there
    BCDurbin's Avatar
    BCDurbin Posts: 27, Reputation: 1
    New Member
     
    #8

    Mar 25, 2008, 11:58 AM
    So far nothing - I always wonder if I am doing it right though - so I will continue testing some other wires and make sure I can get voltage somewhere! - I have the schematic as well, that is helping me too, but right now I cannot get 24 V at the valve.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #9

    Mar 25, 2008, 12:01 PM
    Trace the wiring back through the controls to find the device that is preventing the flow of the voltage to the valve. Pressure switches can cause this problem as well as other controls.
    BCDurbin's Avatar
    BCDurbin Posts: 27, Reputation: 1
    New Member
     
    #10

    Mar 27, 2008, 09:13 AM
    Quote Originally Posted by hvac1000
    Trace the wiring back thru the controls to find the device that is preventing the flow of the voltage to the valve. Pressure switches can cause this problem as well as other controls.
    I can get 110 at the transformer and 24 on the other side, to the circuit board.
    I am guessing there is a sequence of events - I am getting 24 volts to my limit switches and pressure switch. The pressure switch works because the HSI comes on but then I do not get any voltage (24) to my ROS's thus no voltage to my gas valve. And then no flame so no voltage to the Flame Sensor.
    I'm going overboard with this - it's problably something simple! I just can't believe it's something wrong with the circiut board.

    Thanks - BCD
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #11

    Mar 27, 2008, 04:39 PM
    ((I do not get any voltage (24) to my ROS's thus no voltage to my gas valve.))

    Looks like you have narrowed the problem down. Wherever the voltage stops that is the area of the problem.
    BCDurbin's Avatar
    BCDurbin Posts: 27, Reputation: 1
    New Member
     
    #12

    Apr 1, 2008, 08:41 AM
    Quote Originally Posted by hvac1000
    ((I do not get any voltage (24) to my ROS's thus no voltage to my gas valve.))

    Looks like you have narrowed the problem down. Wherever the voltage stops that is the area of the problem.

    Thanks for all your help - I'll order a new circuit board and see if that helps - with that I'm only $140 invested in the problem so far! I'll let you know if it fixes it! - BCD
    BCDurbin's Avatar
    BCDurbin Posts: 27, Reputation: 1
    New Member
     
    #13

    Apr 3, 2008, 05:55 PM
    Quote Originally Posted by BCDurbin
    Thanks for all your help - I'll order a new circuit board and see if that helps - with that i'm only $140 invested in the problem so far! I'll let you know if it fixes it! - BCD

    Well that didn't fix it! Everything is the same except I get a solid status light on my new circuit board. Still no gas - and I'd bet I have gas pressure cause I still have hot water off the same gas line. My only consolation is that it's going to be 74 tomorrow. I guess Ill call in the pros now and see what they say - unless there are any more suggestions! - BCD
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #14

    Apr 4, 2008, 12:39 AM
    Is there 24 volts getting to the gas valve? If so and the valve does not open the gas valve is bad. I wonder if this unit was hit by a electrical surge. This can cause a failure of more than one part at a time.
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #15

    Apr 5, 2008, 04:58 PM
    Two things you need for sure on a gas furnace 24v. On the gas valve when you call for heat at the thermostat and gas pressure AT THE INLET SIDE OF GAS VALVE even if the cook stove and water heater is working. If you have inlet pressure and not manifold pressure with 24v on the gas valve it's a bad gas valve.
    BCDurbin's Avatar
    BCDurbin Posts: 27, Reputation: 1
    New Member
     
    #16

    Apr 17, 2008, 12:53 PM
    Quote Originally Posted by hvac1000
    Is there 24 volts getting to the gas valve? If so and the valve does not open the gas valve is bad. I wonder if this unit was hit by a electrical surge. This can cause a failure of more than one part at a time.
    The new circuit board may have fixed the problem - I got 24 volts all around where I needed it but it still was not working - until I reset my first ROS. I hope after all the money spent, that a bad circuit board tripped the first ROS and was waiting for me to find it! If not then it's a lesson learned - check your roll out switches first!

    Any way, I have HEAT - just in time to turn the AC on!

    Thanks again for your responses. - BCD

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Goodman furnace HSI does not glow, burners never light [ 3 Answers ]

I have a Goodman gas-forced air furnace, about 10 years old. I have power to the main control panel (part# 18099-13) and gas is "on". In the furnace sequence posted by sticky, I am having problems at the step where the hot surface ignitor "glows" to light the burners. All other steps, such as the...

Gas furnace has an intermittent pilot, pilot lights, furnace tries to start [ 3 Answers ]

Have a 25 plus year old furnace pilot will start when signal sent furnace tries to start makes noise as it tries over and over but will not start. Thanks

Gas furnace lights, goes off after a minute or so, then blows cool air [ 6 Answers ]

We just noticed this problem today, on the coldest day it has been this winter. Don't know if the cold has anything to do with this issue or not, but I don't think so after reading through the forum. The problem appears to be that our furnace (about 15-20 years old, Magic Chef/Comfortmaker Ultra II...