    Gas Pipe Size Changes
    In the process if doing an extensive remodel and I'm upgrading my natural gas plumbing. I've got the sizing all worked out but I'm confused about where sizes should change. My gas meter has a 3/4 inch output. I understand that I can connect my new 1 1/4 inch pipe as long as it is "close" to the meter. In other words there really is no need to replace the meter with one that has a 1 1/4 inch output.
    I'm adding a 200,000 BTU tankless water heater that has a 3/4 inch gas inlet. So my question is where should I transition from 1 1/4 inch back down to 3/4? I'm mounting it high on the wall in a new laundry room so the gas line will exit about 5 feet up the wall. Should I run the 1 1/4 inch up that wall, or could I make the reduction in the crawl space before it turns up that 5 feet? I'm not too eager to cheap out and do whatever is easy, but I don't want to make it more complex of there is no value.

    Pipe Sizing:
    75' of 1 1/4 inch from meter to junction just below Water heater
    5' of 1 /1/4 (?) from junction to 200k BTU Water Heater and 25k BTU gas dryer
    25' of 3/4 inch from junction to 50k BTU cooktop
    20' of 3/4 inch from junction to 50k(?) BTU gas logs

    Thanks!
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #2

    Jan 28, 2008, 12:59 PM
    Hey Oregon.

    If I understand you, I would run 11/4" pipe over toward the heater and then reduce to a 11/4" x 1" x 1" tee (1" up to heater..would like to see this have a drip tee with a 3.5 inch drip leg (nipple) with a cap for condensation). Then run 1" over toward the cooktop and install a 1"x 3/4"x3/4" tee (3/4" up to cooktop) and then 3/4" over to gas log.

    I would connect the heater by 3/4" shutoff (always 1st so can shut gas to unit then break union to work on) and 3/4" union as I would all gas appliances ( the union/shutoff ).

    The drip tees I am talking about are designed to capture any condensation that may accur... they are primarily used going from a horizontal to a vertical... so off the 11/4" union as I would all gas appliances ( the union/shutoff ).

    The drip tees I am talking about are designed to capture any condensation that may accur...they are primarily used going from a horizontal to a vertical...so off the 11/4"x1" tee I would go vertical by using a 1"x1" long nipple) and a tee fitting so I could go vertical 1" space nipple (about 2.5" drip leg (requires a 3.5 inch nipple) and cap. Any more questions just ket us know!

    In order to do an accurate job here I would need to know all gas appliances in the house and the distance from the meter for each... let me know if you want this done.

    Hey, if this helped, please RATE THE ANSWER below. Thank you.
    Some_Mich_Guy's Avatar
    Some_Mich_Guy Posts: 1, Reputation: 1
    New Member
     
    #3

    Nov 22, 2011, 10:39 PM
    Hey--I found this answer via a search; I realize that the thread is from 2008, but I was wondering where this issue (whether or not/how you can go from a smaller-dia. Pipe @ the point of delivery to a larger-dia. Pipe) is covered in, e.g. the Nat'l Fuel Gas Code (the one which is the basis for that area of Michigan's code... where I live)..

    I also am adding a tankless water heater, and, using the branch length method, it shows that I need a larger size of pipe from the point of delivery to the branch with the new water heater (moving up from 1" to 1.25"; this is assuming that I can use Table 6.2(b) rather than 6.2(a) for my Sch. 40 metallic pipe... otherwise, I have to move up to 1.5"). So that's the basis for this add-on q. Thanks!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Pipe size and connection type [ 2 Answers ]

I am plumbing a bath in my unfinished basement. The drains are existing but need to plumb the hot and cold water supply. The question is, the house has been plumbed with pex (its a flexible colored pipe - red for hot and blue for cold). Should I use this type of pipe? If so, should I run 3/4" to...

Pipe size? [ 2 Answers ]

I live in san francisco and am adding a lavitory sink I plan to connect to current shower drain with a wye and loop vent through same what size pipe do I need and what is the best way to support it ? Sink will be 4 1/2 feet from shower drain thank you tallgrass:o

Natural gas pipe in bsmt is touching gas pipe [ 2 Answers ]

I just bought a house and in the basement the single wall furnace flue is touching the dark iron natural gas pipe, just before it enters the brick chimney , the water heater also has single wall flue that runs through wood structure. The previous owner put coffee cans around the flue, he cut off...

Pvc pipe size per code [ 1 Answers ]

I have a 1982 double wide cavco that sits above ground. I had a slow drainage problem in the tub and shower. I called the plumber out, actually three of them worked on the issue, and was not resolved. The supervisor explained that after trying for four hours, they were going to call it quits. He...

Question about pipe size [ 1 Answers ]

Hi,everyone, I am confused about the pipe size for a urinal. The specification for one brand flushometer says that: 1" IPS angle stop and 1 1/4" top spud I don't know where the top spud is. If my water supply line pipe size is 1 1/4" IPS, should i find a flushometer with 1 1/4" angle stop or 1...


View more questions Search