    Short Furnace Running Cycles
    My furnace only runs for 15-30 seconds at a time. It will kick off and then fire up 2 minutes later for about another 30-40 seconds. The desired temperature is maintained but the very short on and off cycles are very annoying. We were told it may be our thermostat so we installed a new one and we are still having the same problem. Is there anything that can be done the have the furnace run for longer, less frequent cycles?
    Eric D's Avatar
    Eric D Posts: 98, Reputation: 4
    Junior Member
     
    #2

    Jan 11, 2008, 08:54 PM
    Where is the thermostat located? This could be a factor if near a vent. The furnace might be oversized for the job. Some furnaces can be re-jetted to reduce the BTU level to allow for longer run times. Has the furnace always done this, or is this something new?

    Eric D
    akman's Avatar
    akman Posts: 6, Reputation: 1
    New Member
     
    #3

    Jan 11, 2008, 11:55 PM
    Is this an oil furnace? Sometimes if the burn pan is out of level ( spot welds can break and the pan is canted) the furnace will automatically shut the burn cycle off.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Jan 12, 2008, 12:49 AM
    I would check your fan/limit control. It has probably gone out of calibration. In many cases they are adjustable but they are not that expensive to replace.

    For test purposes only you can jump the limit feature (safety device) out and run the burner to see if it runs a longer time. If so replace limit in not kep looking for the real problem.

    Caution if limit needs replacing do not run jumped out for any great length of time. Your furnace could go to terminal melt down if the blower would fail.
    Frdbrkl's Avatar
    Frdbrkl Posts: 94, Reputation: 7
    Junior Member
     
    #5

    Jan 12, 2008, 06:27 AM
    Quote Originally Posted by JenScammy
    My furnace only runs for 15-30 seconds at a time.
    Is it a boiler or a furnace?

    Quote Originally Posted by JenScammy
    It will kick off and then fire up 2 minutes later for about another 30-40 seconds. The desired temperature is maintained but the very short on and off cycles are very annoying.
    If it's a boiler, look at your pump and see if it's working. If not, the pump needs replacing. If you can't tell, feel the pipes. If they are smoking hot close to the system, but get colder the further you get from the boiler, it's definitely a pump related problem.

    Quote Originally Posted by JenScammy
    We were told it may be our thermostat so we installed a new one and we are still having the same problem.
    Thermostats are only switches. If it turns the unit on, it's typically not the stat. Thermostats are replaced in error more than any other component on the system. And for ease of troubleshooting, always use Honeywell, or White-Rodgers as a second choice. Avoid Lux, MapleChase, and "toms house of thermostats" type models.

    Quote Originally Posted by JenScammy
    Is there anything that can be done the have the furnace run for longer, less frequent cycles?
    Definitely. Locating the cause may be tricky though.

    If it's a furnace... check your filter, make sure all vents are opened-return AND supply. Check the temperature of the air coming out of the vents when it IS running. Clean flame sensor (just in case) with clean steel wool. Unfortunately, the symptoms you are describing are vexing to troubleshoot without being onsite-that's why I suggested "boiler" (that and a lot of homeowners don't discern the difference).

    If it's a furnace, it sounds like it may be "cycling on the limit" indicating an overheating of the unit. If the above suggestions don't remedy the situation, contact a professional, as safeties are NEVER to be ignored.

    Do you have a model number and manufacturer? This helps greatly...
    gravesite's Avatar
    gravesite Posts: 7, Reputation: 1
    New Member
     
    #6

    Jan 12, 2008, 06:21 PM
    Quote Originally Posted by JenScammy
    My furnace only runs for 15-30 seconds at a time. It will kick off and then fire up 2 minutes later for about another 30-40 seconds. The desired temperature is maintained but the very short on and off cycles are very annoying. We were told it may be our thermostat so we installed a new one and we are still having the same problem. Is there anything that can be done the have the furnace run for longer, less frequent cycles?
    You should get a ohm meter and hook it to your wires in place of your thermostat and get the reading from the ohm meter this number is what your heat anticapater should be set on in your themostat so that your furnace will cycle properly
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #7

    Jan 12, 2008, 11:41 PM
    ((To get proper heat anticipator settings requires an amp clamp and 10 wraps around the clamp in series with the gas valve. This is not a heat anticipator issue, as the unit is running for 30 seconds or so.))

    You are correct but I find it much easier and more accurate to use a miliamp meter. No wraps and more accurate.
    Frdbrkl's Avatar
    Frdbrkl Posts: 94, Reputation: 7
    Junior Member
     
    #8

    Jan 13, 2008, 07:46 AM
    Quote Originally Posted by hvac1000
    ((To get proper heat anticipator settings requires an amp clamp and 10 wraps around the clamp in series with the gas valve. This is not a heat anticipator issue, as the unit is running for 30 seconds or so.))

    You are correct but I find it much easier and more accurate to use a miliamp meter. No wraps and more accurate.
    My bad... I don't personally use them, as I carry my amp clamp everywhere and have constructed a nice little "rig" that mounts fairly quickly... no more wrapwrapwrapwrap crap. I also wanted to straighten out the "ohm meter" post to keep people from chasing their tails. Gravesite was probably referring to a maMeter instead of an ohm meter.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Goodman Furnace -takes 2 Or 3 Ignition Cycles before Stays Running [ 2 Answers ]

Hi,hope you can help me out.i have a goodman manufacturing forced air furnace that i believe is giving me a warning sign of a future failure.what has happened is in this order,1st one morning the thermostat showed that the furnace was on and it was'nt.turned it off and then back on at the...

Intertherm Furnace Cycles Off and On [ 8 Answers ]

Have a Intertherm furnace in my mobile home that is about 10 years old and has worked fine until last year. It will cycle the blower off and on a couple times during the warming cycle until it reaches a certain temp in the house. If it is above a certain temp in the house it runs fine and works...

Furance short cycles [ 2 Answers ]

I have a carrier 8000 furnace model#58ZAV050-08-serial#3395A20997. In the past ten days the furnace cycles through and run for a while then shuts down.I'm not getting any LED codes. The flame sensor looks good, the high pressure switchseems OK,no indication of a cracked exchanger the flames in...

Furnace heat cycles on/off [ 1 Answers ]

We have an old furnace,not quite sure how old.It is a Bryant Quietair.I noticed tonight the burners would light,stay lit for a few seconds(30-40secs.),then go out,and then relight a few seconds later.The fan is running throughout the whole process like it should.This goes on constantly.What is...

Furnace cycles evry two minutes [ 5 Answers ]

I have a 15 year old 70000 BTU high efficiency gas furnace, and it is cycling every 2-3 min and the house is COLD (about 10 degrees lower than comfortable) The small exhaust fan comes on, the igniter turns on, the pilot turns on, the pilot sensor heats up and then the main gas goes on and burns,...


View more questions Search