    Vent Safety Switch Trips
    I just installed a new Williams double side direct top vented wall heater. When I put the cover on the heater it trips the vent switch after 5 -7 minutes. If I leave the cover off it runs fine. Help!
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jan 5, 2008, 04:47 AM
    Check your gas pressure. It might be to high allowing the unit to over fire causing overheating/spillage/vent trip. I am sure you already checked the vent to be sure it is clear of any obstruction?
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #3

    Jan 5, 2008, 06:29 AM
    Wall heaters have to be vented exactly as specified in the manufactures installation booklet or you can have problems with tripping on the vent safety switch.
    In the installation guide it will tell you to use type "B" vent , this is double wall pipe , if you use a single wall pipe it will not vent properly or if the vent does not terminate above the roof at the proper highth above the floor, it will not vent properly.
    Wall furnaces are the most dangerous furnaces that are installed in peoples homes because the carbon monoxide gases can enter the living space if not vented properly and kill you. These gases are odorless and can cause vomiting, brain damage and death. Don't take a chance with this furnace , be sure it is in stalled properly. Good luck, Mike

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Safety switch keeps tripping [ 4 Answers ]

I have a Carrier unit with a Becket Model "AFG" oil burner. Unit was installed 5/2002. It was given its maintenance service on 11/15/07 by Carroll Ind. I was delivered 100 gal of oil the week before Christmas around the 18th. System has been working fine until 2 weeks ago when the Honeywell...

Bryant 394GAD Vent Safety Switch Trips [ 1 Answers ]

I have a Bryant 394GAD that runs fine for days, then begins to have issues with the Vent Shut Safety Switch tripping and shutting down the flame. The fan continues to run and blow cold air throughout the house. If I reset the switch, the burners will come back on and the furnace will run. ...

New switch trips breaker [ 1 Answers ]

I added a plg strip to an existing circuit,and plugged fluorscent fixture into strip.I then wired a switch and plugged it into strip. Off the switch I ran two 14/3 cables with plugs on the end to be used with portable lights.When switch is on everything works fine, but when I turn switch to off...

Light switch trips breaker [ 4 Answers ]

Here's question number 2 in switching out fans and light fixtures. I replaced the ceiling fan in my son's room with one from our previous home. After getting everything wired rather difficult because of some very short wires, the ceiling fan will work with the remote, but using the wall switch...

GFI trips when fliping switch [ 5 Answers ]

I have an outdoor fountain with a pump that is pluged into a new outlet next to the pump. I connected that outlet to an outdoor switch on the porch so I can turn the punp on and off without going to the fountain. I taped into an existing outdoor outlet on the porch and put the switch next to...


View more questions Search