    Nagbert's Avatar
    Nagbert Posts: 1, Reputation: 1
    New Member
     
    #1

    Jan 4, 2008, 10:19 AM
    Rheem Furnace Blower Stays On
    I have a Rheem Criterion II (Model RGPH 07NAMGR) with the main furnace blower that runs continuously. The IFC board (62-24084-82) is giving me the three blink error (middle green light between a green and orange bulb) which I believe indicates an open limit switch. I have check the three limits (manual resets) in the burner compartment. Each of the reset switch is depressed. I did check each of the limit switch with a meter and there is no resistance indicated from the two connectors on the limit.

    Is it possible that it is the flame sensor? Is the flame sensor the single rod with a single red lead near the burner?

    I've check the filter and seems to be okay. Is there any thing else I should check?

    Thanks
    NorthernHeat's Avatar
    NorthernHeat Posts: 1,455, Reputation: 132
    Ultra Member
     
    #2

    Jan 4, 2008, 04:26 PM
    There is also a main limit on the back wall and often another in the blower compartment. Limits trip due to poor airflow. Read the FAQ at very top of heating page for more info and pictures of limits and airflow problems.
    maubele's Avatar
    maubele Posts: 1, Reputation: 1
    New Member
     
    #3

    May 11, 2012, 04:40 PM
    I have a Rheem Criterion ll (Model RGHP-07NAMGR) the main furnace blowers is always on. The IFC board the top green light is on, middle green light blinks and the orange bottom light isn't on. Where are the 3 limit switches so I can manually reset them to see if this solves the problem. Thank You

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Rheem furnace blower motor won't turn on [ 2 Answers ]

My furnace blower motor will not turn on. The troubleshooting guide says to replace blower motor but the diagnostics says the Limit Switch is Open any ideas

Furnace Blower stays on too long. [ 1 Answers ]

Hello. I have a Honeywell Electric furnace. Model # AR36-1 The blower stays on too long after furnace shuts off and cold air blows out. Any ideas how to fix it? Thanks.

Furnace Blower stays on far too long [ 1 Answers ]

We have an older Tappan ANS Z21.47 furnace, circa 1979. When the cooler weather season started this year we turned on the heat and noticed that once the house had reached the correct temperature then the blower would remain on and blow cooler air for at least 20 minutes afterwards. We had read...

Furnace Blower stays on, no heat [ 2 Answers ]

Hello, I have an older Bryant furnace model # 396gadd36075. I turned on the heat the other day and the no heat. I notice the unit had been turned off (pilot was not lit), apparently by the service company I use when they came to do the spring check for the AC. I followed the instructions to...

Furnace fan blower stays on too long. [ 1 Answers ]

The fan blower for a coleman mobile home furnace stays on and begins to blow cold air before shutting off, how do I know if the fan/lower limit switches are the right ones? Model # 7680C856 80,000 BTU.


View more questions Search