    Breaker triping
    I have just installed a heat pump to my indoor swimming pool however after running fine for the first two months, the breaker has begun to trip at any given time.

    The heat pump is a 5.5kw 220volts 25amps which I wired with 4mm three way wiring (neutral, live & earth). I have installed a 20amp 6ka hy mag breaker(orange flip switch) to the mains board of the house.
    The way I have explained the installation was given to me by the suppliers of the heat pump & they in turn are lost for words, please help as I am not sure what I did wrong.

    Regards

    Andredev
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #2

    Jan 1, 2008, 01:33 PM
    So you installed a 20 amp breaker for a 25 amp pump?
    smearcase's Avatar
    smearcase Posts: 2,392, Reputation: 316
    Ultra Member
     
    #3

    Jan 1, 2008, 01:43 PM
    Neutral, live and earth for 220V?
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #4

    Jan 1, 2008, 02:30 PM
    andredev didn't favor us with his location, but that is how they do things on the East side of the Atlantic.

    I don't have a table for 4 mm wire, but it is larger than our #8, usually good for 40 amps if copper. Check the rating for the 4 mm and type of cable you used. If it is OK, try a heavier breaker.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Replacing Circuit Breaker with Higher AMP Breaker [ 8 Answers ]

Excuse me, I did look at the code book as is suggested in your Sticky. The NFPA may answer this question, but I am not knowledgeable enough to recognize it: Our offices are upstairs in an older (renovated home) building with modern wiring. We have 4 computers, 3 printers, and miscellaneous with...

Carrier unit popping and triping not cooling [ 2 Answers ]

Our unit is not cooling and triping outside breaker, a carrier tech came out and said " system check good, charge good, amp draw on compressor good 18, so my husband replace the outside fuse and cooled well but know it is still running ,not cooling and tripping breaker, and know there is a pop...

New 15A breaker trips main 100A breaker [ 6 Answers ]

Hi, I've been finishing my basement and I added a few 15A breakers One room has 8 outlets in series with the first starting about 6 feet from the main panel. There is currently no load on this outlets. When installing the drywall I accidentally shorted the outlet closest to the panel. It...

Replacing a circuit breaker with a GFI breaker- q on neutrals [ 1 Answers ]

In process on installing withquestion on neutral wires. Do you take the neutrals out of the in the main panel neutral and put them in into the breaker where its labelled "load neutral terminal" and only have the neutral "pig tail" to the panel neutral bar? Thanks!

Power in part of house goes dead w/out triping breaker [ 3 Answers ]

Hello, great site, use it more than I thought I would. Question: The electricity in part of my house will go dead without tripping the breaker for those rooms and then will come back on within 30-60sec by itself, lights have been dimming as if a dip in voltage has occurred. Thanks Gbrown


View more questions Search